I know, enclosing these stairs creates a problem. But Todd, you think if a
building has exterior, non-combustible stairs (such as say a fire exit),
then it should be sprinklered? I haven't thought of it as that way, that is
why I'm asking.
Tony

On Thu, Oct 18, 2018 at 7:39 AM Fpdcdesign <[email protected]> wrote:

> Remember, these stairs are a means of egress. If these stairs were
> enclosed as part of the original building construction, would you sprinkler
> it?
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080 (ofc)
> 860-553-3553 (fax)
> 860-608-4559 (cell)
>
>
> On Oct 17, 2018 at 8:38 PM, <Tony Silva <[email protected]>> wrote:
>
> The building and stairs are non-combustible. If the stairs are not heated
> can it be considered outside the building envelope?
>
> Which leads to a side observation. We provide sprinklers for balconies and
> below combustible overhangs that are over 4 feet wide. And won't that be
> outside the building envelope? So would not sprinklering outside the
> building envelope be a valid argument?
>
> Tony
>
> On Wed, Oct 17, 2018 at 5:09 PM Fpdcdesign <[email protected]> wrote:
>
>> If the enclosure is part of the building envelope, then it should be
>> sprinklered
>>
>> Are the stairs combustible?
>>
>> Todd G Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860-535-2080 (ofc)
>> 860-553-3553 (fax)
>> 860-608-4559 (cell)
>>
>>
>> On Oct 17, 2018 at 6:58 PM, <Tony Silva <[email protected]>> wrote:
>>
>> I have been asked this question, so I thought I will get the opinion of
>> the forum. An NFPA 13, 2013 building has emergency stairs on the exterior
>> of the building. Now it has been decided to enclose it, but will remain
>> unheated.
>>
>> (1) Is it required to be sprinklered, if not enclosed?
>> (2) Would the answer to (1) be different if enclosed?
>>
>> Tony
>> _______________________________________________ Sprinklerforum mailing
>> list [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
> _______________________________________________ Sprinklerforum mailing
> list [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to