The bulk of the storage area is ceramic or porcelain tile, in wrapped boxes, on 
wood slat pallets.

However there are “some” vinyl floor tiles (packaged the same way) and “some” 
rolled rugs and carpet squares.


John Irwin
Quick Response Fire Protection

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Larry Keeping
Sent: Thursday, November 29, 2018 12:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Mixed rack storage

Whoa there!

The Chapter 13 only covers plastic to storage to 5 ft in dedicated storage 
facilities or Miscellaneous Storage of Plastics to 12 ft.

My understanding is that the area in question is designated for storage (ie. it 
is a 4600 sq ft warehouse area), so for plastics to 12 ft on racks you need to 
go to Chapter 17.

Best regards,

Larry Keeping

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of John Irwin
Sent: November-29-18 10:48 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Mixed rack storage

I agree with this, except it calls for one level of in-racks.

John Irwin
Quick Response Fire Protection

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of cw bamford
Sent: Thursday, November 29, 2018 10:36 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Mixed rack storage

Calc seperate areas.

group A plastics on racks UNDER 12’

using 2013 edition of NFPA 2013
Table 13.2.1
Exposed -- Unexpanded --  Rack
>10' to 12'
OH2

Please check my work.

onto
Ceramic Floor Tiles
It's not just the commodity, It's how they are stored and moved on the racks
? in cardboard ? with some Styrofoam? Encapsulated? solid shelves

Chuck Bamford SET



On Wed, Nov 28, 2018 at 11:05 AM John Irwin 
<jir...@quickresponsefl.com<mailto:jir...@quickresponsefl.com>> wrote:
I am working on a flooring retail building that has a 4,600 sqft warehouse. 
Roof is at 30’ and they want to store to 20’. They will have vinyl flowing and 
rolls of rug and carpet, as well as ceramic and porcelain tile. I believe I 
have determined that the vinyl and rolls of rug equate to Group A, non-expanded 
plastics. My question is this … is it permissible for the client to storage all 
their group A plastics on racks UNDER 12’ and their ceramic floor tiles on the 
racks OVER 12’ and to then calculate the roof system for the lesser, ceramic 
tile storage?



John Irwin

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>