If the state or jurisdiction has adopted NFPA #24, then section 6.6 covers 
valves.



  *   Sprinkler “riser” supply - See NFPA #24 Section 6.2.11 for valve 
requirements for each of the fire sprinkler system supplies. The typical valve 
is a PIV, but other arrangements are also permitted.


  *   “Loop” section valves – See NFPA #24, Section 6.6.1 for valve 
requirements within the “loop”. The typical valve will be a street valve, one 
per six connections.


  *   Hydrant valves – See NFPA #24, Section 7.1.1.1. A valve shall be 
installed in the hydrant connection, within 20-feet of the hydrant.

If the jurisdiction has adopted valves into their own fire code, or for example 
the purveyor of water likely has their own service standards to be met as a 
condition of receiving water, then they should be able to copy/articulate those 
to you.

Hope this helps.
Andrew Steele