I’ve seen up to five control valves required on a line to a single
sprinkler system. First the road valve where the tap has been made, then a
vault with the two valves on the back flow device, then a yard PIV and
finally a riser control valve. Considering that the single biggest source
of system failure adding all these valves seems like a bad idea and
demonstrates the importance of the main drain test. Now if we could only
get ALL the ITM guys to regularly do it and to educate them ALL, not only
as to why it's needed but also how to identify and read the meaning of the
anomalies.

On Mon, Dec 3, 2018 at 1:22 PM Steele, Andrew <[email protected]>
wrote:

> If the state or jurisdiction has adopted NFPA #24, then section 6.6 covers
> valves.
>
>
>
>
>
>    - Sprinkler “riser” supply - See NFPA #24 Section 6.2.11 for valve
>    requirements for each of the fire sprinkler system supplies. The typical
>    valve is a PIV, but other arrangements are also permitted.
>
>
>
>    - “Loop” section valves – See NFPA #24, Section 6.6.1 for valve
>    requirements within the “loop”. The typical valve will be a street valve,
>    one per six connections.
>
>
>
>    - Hydrant valves – See NFPA #24, Section 7.1.1.1. A valve shall be
>    installed in the hydrant connection, within 20-feet of the hydrant.
>
>
>
> If the jurisdiction has adopted valves into their own fire code, or for
> example the purveyor of water likely has their own service standards to be
> met as a condition of receiving water, then they should be able to
> copy/articulate those to you.
>
>
>
> Hope this helps.
>
> Andrew Steele
>
>
>
> *Web <http://www.daytonohio.gov/>*   | *Twitter
> <http://twitter.com/cityofdayton>*  |  *Facebook
> <http://www.facebook.com/pages/Dayton-OH/City-of-Dayton-Ohio/47806554955>*
> |  *YouTube <http://www.youtube.com/cityofdaytonohio>*  |  *Nixle
> <http://www.nixle.com/>*  |  E-mail Newsletters
> <http://visitor.constantcontact.com/d.jsp?m=1101627103042&p=oi>
>
>
>
>   ­­
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to