All - I'm looking at a closed head foam/water design at the moment, 2016 
edition of 409, Group II hangar - utilizing section 7.6 for the closed head 
foam/water system via section 7.1.1(4).  Section 7.7 goes into detection and 
actuation.  Detection is being provided via waterflow as allowed by 7.7.2.  My 
question involved manual activation stations.  In this instance, where only a 
closed head foam/water system is provided, there appears to be no means of 
manual activation given you are relying solely on sprinkler activation and have 
no ability to put a solution to the fire other than sprinkler RTI.  Is this in 
direct conflict with 7.7.5 requiring manual activation stations or have I 
completely missed something?

Thank you in advance.

Spencer Tomlinson
Principal, PE