If you are spraying across you are good. Just can’t be at the low end shooting up.
Travis Mack, CFPS, CWBSP, RME-G, SET 480-505-9271 MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone > On Feb 21, 2019, at 4:21 PM, Matthew J Willis <[email protected]> wrote: > > 8.7.4.2.2 (16) notwithstanding.. > > Are we allowed to install sidewalls along the slope (running with the slope), > if the general requirements of 8.5 are met? > > In other words, think of a church assembly area. Sidewalls up the slope. > First one at 10’ AFF, next at 12’ AFF, etc. Spraying perpendicular (across) > the slope. > > I always thought the 2/12 was to avoid sprinklers trying to spray up the > slope from down low. > > Wanting to clear my mind…. > > R/ > Matt > > > Matthew J. Willis, CWBSP > Design Manager /3-D Specialist > Rapid Fire Protection Inc. > 1530 Samco Road > Rapid City, SD 57702 > Office-605.348.2342 > Direct Line-605.593.5063 > Cell-605.391.2733 > Fax:-605.348.0108 > > <image001.png> > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org