I happily stand corrected. Deflector must be oriented parallel to ceiling. But, 
if slope exceeds 2:12 it must be located at the high point. 

Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Feb 21, 2019, at 4:41 PM, Matthew J Willis <[email protected]> wrote:
> 
> I think that is what is happening.
> I know I read it, but can’t find it. Now.
>  
> Hazards of remembering stuff going back may revisions.
>  
> Thanks guys!
>  
> R/
> Matt
>  
> Matthew J. Willis, CWBSP
> Design Manager /3-D Specialist
> Rapid Fire Protection Inc.
> 1530 Samco Road
> Rapid City, SD 57702
> Office-605.348.2342
> Direct Line-605.593.5063
> Cell-605.391.2733
> Fax:-605.348.0108
>  
> <image001.png>
>  
> From: Sprinklerforum <[email protected]> On 
> Behalf Of Steve Leyton
> Sent: Thursday, February 21, 2019 4:32 PM
> To: [email protected]
> Subject: RE: Sloping Sidewalls
>  
> I believe the cross-slope listings were pulled and the only allowed 
> configuration is DOWN-slope.
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Travis Mack
> Sent: Thursday, February 21, 2019 3:31 PM
> To: [email protected]
> Subject: Re: Sloping Sidewalls
>  
> If you are spraying across you are good. Just can’t be at the low end 
> shooting up. 
> 
> Travis Mack, CFPS, CWBSP, RME-G, SET
> 480-505-9271
> MFP Design, LLC
> "Follow" us on Facebook: 
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
>  
> Sent from my iPhone
> 
> On Feb 21, 2019, at 4:21 PM, Matthew J Willis <[email protected]> wrote:
> 
> 8.7.4.2.2 (16) notwithstanding..
>  
> Are we allowed to install sidewalls along the slope (running with the slope), 
> if the general requirements of 8.5 are met?
>  
> In other words, think of a church assembly area. Sidewalls up the slope. 
> First one at 10’ AFF, next at 12’ AFF, etc. Spraying perpendicular (across) 
> the slope.
>  
> I always thought the 2/12 was to avoid sprinklers trying to spray up the 
> slope from down low.
>  
> Wanting to clear my mind….
>  
> R/
> Matt
>  
>  
> Matthew J. Willis, CWBSP
> Design Manager /3-D Specialist
> Rapid Fire Protection Inc.
> 1530 Samco Road
> Rapid City, SD 57702
> Office-605.348.2342
> Direct Line-605.593.5063
> Cell-605.391.2733
> Fax:-605.348.0108
>  
> <image001.png>
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to