It’s my understanding that the AHJ was aware the water supply in the area was 
not good but there was never a discussion of a water tank during any of the 
pre-development meetings. I will reach out to him again and let him know it 
looks like that’s where were headed….

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum <[email protected]> On Behalf 
Of Bruce Verhei
Sent: Friday, March 22, 2019 8:01 PM
To: [email protected]
Subject: Re: Water Tank

Hopefully you are prepping for discussion with AHJ’s. Was tank a topic at 
pre-development meeting?

Best.

Bruce Verhei

On Mar 22, 2019, at 15:35, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:
If the inference is that the presence of a standpipe system would impose a hose 
stream allowance on the sprinkler system demand, that isn't correct. However 
you would have to design for the standpipe demand or the sprinkler demand which 
ever is greater.



Steve Leyton

(Sent from my phone; please excuse typos and voice text corruptions.)



-------- Original message --------
From: "Mark Sornsin [FAR]" 
<[email protected]<mailto:[email protected]>>
Date: 3/22/19 2:21 PM (GMT-08:00)
To: 
"'[email protected]<mailto:[email protected]>'"
 
<[email protected]<mailto:[email protected]>>
Subject: RE: Water Tank

If you DON’T have hydrants downstream, do you have a standpipe with hose 
connections and an automatic supply?  I’m guessing not.  If not then you don’t 
need the hose allowance (since there’s no place for hoses to be used).


<image07cf41.JPG><http://www.SummitCoUS.com>


Mark Sornsin
Sr. Fire Protection Engineer
Direct: 701-499-1391
Cell: 701-526-8585


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Wednesday, March 20, 2019 8:57 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Water Tank

If you have hydrants downstream of the tank, do you need to account for site 
fire flow requirements?

If so, you could be looking at 180k gallons and up.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Mar 20, 2019, at 6:45 AM, Brian Harris 
<[email protected]<mailto:[email protected]>> wrote:
Looking for preliminary sizing for a water storage tank. Worst case for this 
particular building would be OH-2. (.2/1500 = 300gpm + 250 hose. 550gpm for a 
minimum of 60 minutes = 33,000 gallons). Per NFPA22 (2013) 5.1.3.1 round it up 
to 40,000 gallons. Does that sound about right?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to