You may also want to consider (NFPA 13 2019) 16.4.1.5 - Water-filed piping 
shall be permitted to be installed in areas where the temperature is less 
than 40F when heat loss calculations performed by a professional engineer 
verify that the system will not freeze.  This lived in chapter 8 with the 
rest of the freezing material previously.  To me this is one of those 
situations where the earlier wording is somewhat liberal, but this section 
tends to make me lean towards a more conservative approach (and assumption 
of intent).  I agree that the maintenance requirements etc might make it 
worth sticking with a wet drop, but getting someone with the initials 
after their name to sign off might be difficult on most projects.


Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]







From:   Kyle.Montgomery <[email protected]>
To:     "[email protected]" 
<[email protected]>
Date:   04/02/2019 11:45 PM
Subject:        Re: [EXTERNAL] Re: Dry Pendents Required in Coolers?
Sent by:        "Sprinklerforum" 
<[email protected]>



BE ADVISED - This email originated outside EMCOR. 

Yeah, once you have to decide between buying 400 pendents or 400 dry 
pendents, it’s a little easier to find yourself on the unconservative 
(non-conservative? Liberal?)... the side that doesn’t want to spend that 
much money. 

I know that isn’t a popular opinion around here sometimes, but that’s how 
it is. Were trying to do the right thing, but I don’t know that there’s a 
good way to justify spending that kind of money just to be on the safe 
side.

But that’s why I ask the question, to get some diverse feedback.

-Kyle M

On Apr 2, 2019, at 7:58 PM, Travis Mack <[email protected]> wrote:

We see these installations in 40k sq ft areas and more. It is a huge cost 
impact. John has a great point. But I don’t have the PE letters behind my 
name so I tend to be a bit on the conservative side. 

Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
www.mfpdesign,com
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Apr 2, 2019, at 7:27 PM, Fpdcdesign <[email protected]> wrote:

John,

I understand your position, but most of this type of installation I see is 
8 sprinklers or less. I don’t think that dry vs standard sprinklers in 
this type of installation have a significant impact to fire protection. I 
would prefer to err on the side of caution. 

Todd G Williams, PE 
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)


On Apr 2, 2019 at 8:50 PM, <John Denhardt> wrote:

 
I fully understand you position but the standard has involved in my 
opinion.  If the piping is not subject to freezing, normal sprinklers and 
a wet system provide better fire protection for the building and the 
owner.  (My personal opinion)
 
The current NFPA 13s allow it.  There is additional language in the 
standard where the system can be exposed to temperatures below 32F for 
short periods.
 
John
 
John August Denhardt, P.E.
301.343.1457 - Mobile
 
From: Sprinklerforum <[email protected]> On 
Behalf Of Fpdcdesign
Sent: Tuesday, April 2, 2019 8:23 PM
To: Sprinklerforum <[email protected]>
Subject: Re: Dry Pendents Required in Coolers?
 
There is a magic number of 40degF that shows up a lot in 13 for wet vs 
dry. I use the same for determining dry pendent vs wet. Under 40degF 
COOLER, DRY PENDENT.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)



On Apr 2, 2019 at 7:51 PM, <John Denhardt> wrote:
I have done it many times and never had an issue.  I receive a letter from 
the cooler box stating the lowest temperature the box can reach.  In most 
cases, there are inter-locks to shut down the refrigeration system down if 
it drops below a preset temperature.  Also, cold air does sink.
 
The cost, reliability (in the past) and future testing makes me not want 
to utilize dry type sprinklers unless absolutely necessary.
 
Thanks,
John
 
John August Denhardt, P.E.
301.343.1457 - Mobile
 
From: Sprinklerforum <[email protected]> On 
Behalf Of Nick Maneen
Sent: Tuesday, April 2, 2019 7:46 PM
To: [email protected]
Subject: Re: Dry Pendents Required in Coolers?
 
I wouldn't. Water begins to expand about 37/38 degrees. The key word is to 
me is "reliably". There are all kinds of scenarios where that temperature 
can drop. The standard is set for a generic situation, not a specific one. 
Also, my own home refrigerator has spots colder than the overall ambient 
temperature. There is too much risk for not enough reward.
Nick Maneen
704-791-7789
 
On Tue, Apr 2, 2019, 7:38 PM Kyle.Montgomery <[email protected]> 
wrote:
2019 NFPA 13:
 
16.4.1.1 Where any portion of a system is subject to freezing AND the 
temperatures cannot be reliably maintained at or above 40 degrees F, the 
system shall be installed as a dry pipe or preaction system.
 
I’m sure this has been discussed before, but the above statement requires 
two conditions:
 
1.       System is subject to freezing
2.       The temperatures cannot be reliably maintained at or above 40 
degrees F
 
It says AND, so it has to be both, not one or the other, right?
 
So if I have a 38 degree F cooler, is it fair to say that it is not 
“subject to freezing”, and thus does not require protection? Is it 
acceptable to drop a wet pendent head into the cooler, rather than use a 
dry pendent?
 
-Kyle M
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing 
list [email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 

_______________________________________________ Sprinklerforum mailing 
list [email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=KryIueb30FAd26l6mZm7ybtajJBrvtYT4CVj0Mtjr-I&s=bmXRAXyl9zqYO7lvPrJQji8RaiTxbYjRsCLSWnptsBQ&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=e8PVyFDy41NUnUgmVz5KkaWBA2KteebWoxq4QNBUYzM&s=dhrn_fmSA9_y43uiyJGBvucyIRBO9sElwhi50WJxGeU&e=




This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to