In my opinion you would have to comply with one of the following.

 

8.12.5.2* Isolated Obstructions Below Elevation of Sprinklers. Sprinklers
shall be arranged

with respect to obstructions in accordance with one of the following:

(1) Sprinklers shall be installed below isolated noncontinuous obstructions
that restrict only

one sprinkler and are located below the elevation of sprinklers such as
light fixtures and

unit heaters.

(2) Additional sprinklers shall not be required where the obstruction is 2
ft (0.6 m) or less in

width and the sprinkler is located horizontally 1 ft (0.3 m) or greater from
the nearest edge

of the obstruction.

(3) Additional sprinklers shall not be required where sprinklers are
positioned with respect to

the bottom of obstructions in accordance with 8.12.5.1.

(4) Additional sprinklers shall not be required where the obstruction is 2
in. (51 mm) or less

in width and is located a minimum of 2 ft (0.6 m) below the elevation of the
sprinkler

deflector or is positioned a minimum of 1 ft (0.3 m) horizontally from the
sprinkler.

(5) Sprinklers with a special obstruction allowance shall be installed
according to their

listing.

 

Thanks,

 




 



 

 

Dane Long, CET
Design Technician | Bamford Fire Sprinkler Co., Inc.
P:    785.825.7710
F:    785.825.0667
A:   1383 W. North Street  Salina, KS  67401



 

 

From: Sprinklerforum <[email protected]> On
Behalf Of James Crawford
Sent: Monday, June 10, 2019 4:39 PM
To: [email protected]
Subject: ESFR Heads and Obstructions

 

We are having a discussion in the office regarding lights and ESFR sprinkler
heads:

 

Is there a distance below the ESFR sprinkler heads where a 24"x 48" light
fixture is no longer an obstruction?

 

This was brought up because we just completed a multi-tenant building and
one of the tenants is installing racking and want the lights to be located
just above the racking which is 10'-0" below the sprinkler heads. Would
these lights still be considered an obstruction? 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  [email protected] <mailto:[email protected]> 

Web www.phaserfire.ca <http://www.phaserfire.ca> 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to