OK, so a quick look shows that for a 1" tee with flow turning 90 degrees, NFPA 
13 gives that an equivalency of 5 ft.

Looking at one of the mechanical tee manufactures (strap on tee) they are 
showing a 1" outlet as being equal to 0.5 ft. of pipe.  (I would have thought 
it to be much higher)

I could not find any EQ L on a thread-o-let.  I figure a mech tee probably has 
similar friction coefficient to a thread-o-let since the only difference 
between the two is welded versus strapped on.

Things that make you go hmmmmmmmm.

Now if we only had a resident mathemagician who could give us the formulae 
needed to solve this kind of conundrum.............


Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Wednesday, June 26, 2019 2:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] Welded outlets - Equivalent feet

Yes.  With regard to this particular question.

[MFP_logo_F]<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com_&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=KJHRFG_rnxzKtj49uCz3wwtL_jZ2FseV_8y_W1HsBQs&s=v6mckuUsFPUZlbR3nrBKtKH9WpvfAf9C_QnJ20BNe00&e=>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=KJHRFG_rnxzKtj49uCz3wwtL_jZ2FseV_8y_W1HsBQs&s=e7BTtHrtfCVCuOVnKCN1AJlgySlV0-8uwo2zf6xBrDQ&e=>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=KJHRFG_rnxzKtj49uCz3wwtL_jZ2FseV_8y_W1HsBQs&s=1Jca0QVbPfPKaWVeEPQWwhGHvRK8RceoMdXSR7BJSA8&e=>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."


From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Prahl, Craig/GVL
Sent: Wednesday, June 26, 2019 11:29 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: [EXTERNAL] Welded outlets - Equivalent feet

Is the PE's problem with the program using tees and you actually using welded 
outlets?

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Wednesday, June 26, 2019 12:58 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] Welded outlets - Equivalent feet

Does anyone have a data sheet with the equivalent feet to use in hydraulic 
calculations.  I have a PE reviewing plans (already approved by local AHJ), 
that is not allowing the fittings used in our program.  Our program just uses 
the tee in NFPA 13.  Never mind we have at least 20 psi margins in all of the 
calculations.

[MFP_logo_F]<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com_&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=0GDypIHm4hWEX5FJjFPfiiQwyZshxiZNeansIQGeBuE&s=vbGTg8l-u3ZxLK_cJKSZf1UvM7sht5xv7LOO6FYlDwg&e=>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>
www.mfpdesign.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=KJHRFG_rnxzKtj49uCz3wwtL_jZ2FseV_8y_W1HsBQs&s=8dhJuo1g3Z9Xe3K9BYipjmARMDD4df0E6edN1dYAO_E&e=>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=0GDypIHm4hWEX5FJjFPfiiQwyZshxiZNeansIQGeBuE&s=1Uq5-rgBvwcZ-E80qF_BVkjOe_wAyED0gdKgf8k394U&e=>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=0GDypIHm4hWEX5FJjFPfiiQwyZshxiZNeansIQGeBuE&s=tKwDQbYzBRk0qFZfVmqdixd9aKmd-gsjqW_oMvycbyU&e=>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."



________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.