https://www.engineersedge.com/fluid_flow/fluid_flow_table_content.htm


Ron Greenman

rongreen...@gmail.com

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)


On Wed, Jun 26, 2019 at 12:57 PM Steve Leyton <st...@protectiondesign.com>
wrote:

> My point exactly.
>
>
>
> *From:* Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Prahl,
> Craig/GVL
> *Sent:* Wednesday, June 26, 2019 12:54 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: [EXTERNAL] Welded outlets - Equivalent feet
>
>
>
> Very possible but that would be kind of worthless info since your greatest
> friction loss is going to be making the turn.
>
>
>
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |
> craig.pr...@jacobs.com | www.jacobs.com
>
> 1041 East Butler Road   Greenville, South Carolina  29606
>
>
>
> *From:* Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> *On
> Behalf Of *Steve Leyton
> *Sent:* Wednesday, June 26, 2019 3:12 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: [EXTERNAL] Welded outlets - Equivalent feet
>
>
>
> I’ll bet a friendly fiddy cent that the .05 ft. value is on the run.
>
>
>
> *From:* Sprinklerforum [
> mailto:sprinklerforum-boun...@lists.firesprinkler.org
> <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Prahl,
> Craig/GVL
> *Sent:* Wednesday, June 26, 2019 12:08 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: [EXTERNAL] Welded outlets - Equivalent feet
>
>
>
> OK, so a quick look shows that for a 1” tee with flow turning 90 degrees,
> NFPA 13 gives that an equivalency of 5 ft.
>
>
>
> Looking at one of the mechanical tee manufactures (strap on tee) they are
> showing a 1” outlet as being equal to 0.5 ft. of pipe.  (I would have
> thought it to be much higher)
>
>
>
> I could not find any EQ L on a thread-o-let.  I figure a mech tee probably
> has similar friction coefficient to a thread-o-let since the only
> difference between the two is welded versus strapped on.
>
>
>
> Things that make you go hmmmmmmmm.
>
>
>
> Now if we only had a resident mathemagician who could give us the formulae
> needed to solve this kind of conundrum………….
>
>
>
>
>
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |
> craig.pr...@jacobs.com | www.jacobs.com
>
> 1041 East Butler Road   Greenville, South Carolina  29606
>
>
>
> *From:* Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> *On
> Behalf Of *Travis Mack, SET, CFPS, CWBSP, RME-G
> *Sent:* Wednesday, June 26, 2019 2:30 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: [EXTERNAL] Welded outlets - Equivalent feet
>
>
>
> *Yes.  With regard to this particular question.*
>
>
>
> [image: MFP_logo_F]
> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com_&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=KJHRFG_rnxzKtj49uCz3wwtL_jZ2FseV_8y_W1HsBQs&s=v6mckuUsFPUZlbR3nrBKtKH9WpvfAf9C_QnJ20BNe00&e=>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
>
> MFP Design, LLC
>
> 3356 E Vallejo Ct
>
> Gilbert, AZ 85298
>
> 480-505-9271
>
> fax: 866-430-6107
>
> tm...@mfpdesign.com
>
> www.mfpdesign.com
> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=JiNFMUwhrGpuKQUdEGxDN2OUDByRHLkEJ2g0BGUrZSg&s=VUUuWqcZpNqJUrqCqzVwQtuteK_BJDO7mui8WJJp-aA&e=>
>
>
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=KJHRFG_rnxzKtj49uCz3wwtL_jZ2FseV_8y_W1HsBQs&s=e7BTtHrtfCVCuOVnKCN1AJlgySlV0-8uwo2zf6xBrDQ&e=>
>
> LinkedIn: https://www.linkedin.com/in/travismack
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=KJHRFG_rnxzKtj49uCz3wwtL_jZ2FseV_8y_W1HsBQs&s=1Jca0QVbPfPKaWVeEPQWwhGHvRK8RceoMdXSR7BJSA8&e=>
>
>
>
> *“**The bitterness of poor quality remains long after the sweetness of
> low price is forgotten.”*
>
>
>
>
>
> *From:* Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> *On
> Behalf Of *Prahl, Craig/GVL
> *Sent:* Wednesday, June 26, 2019 11:29 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: [EXTERNAL] Welded outlets - Equivalent feet
>
>
>
> Is the PE’s problem with the program using tees and you actually using
> welded outlets?
>
>
>
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |
> craig.pr...@jacobs.com | www.jacobs.com
>
> 1041 East Butler Road   Greenville, South Carolina  29606
>
>
>
> *From:* Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> *On
> Behalf Of *Travis Mack, SET, CFPS, CWBSP, RME-G
> *Sent:* Wednesday, June 26, 2019 12:58 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* [EXTERNAL] Welded outlets - Equivalent feet
>
>
>
> Does anyone have a data sheet with the equivalent feet to use in hydraulic
> calculations.  I have a PE reviewing plans (already approved by local AHJ),
> that is not allowing the fittings used in our program.  Our program just
> uses the tee in NFPA 13.  Never mind we have at least 20 psi margins in all
> of the calculations.
>
>
>
> [image: MFP_logo_F]
> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com_&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=0GDypIHm4hWEX5FJjFPfiiQwyZshxiZNeansIQGeBuE&s=vbGTg8l-u3ZxLK_cJKSZf1UvM7sht5xv7LOO6FYlDwg&e=>
>
> Travis Mack, CFPS, CWBSP, RME-G, SET
>
> MFP Design, LLC
>
> 3356 E Vallejo Ct
>
> Gilbert, AZ 85298
>
> 480-505-9271
>
> fax: 866-430-6107
>
> tm...@mfpdesign.com
>
> www.mfpdesign.com
> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=KJHRFG_rnxzKtj49uCz3wwtL_jZ2FseV_8y_W1HsBQs&s=8dhJuo1g3Z9Xe3K9BYipjmARMDD4df0E6edN1dYAO_E&e=>
>
>
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=0GDypIHm4hWEX5FJjFPfiiQwyZshxiZNeansIQGeBuE&s=1Uq5-rgBvwcZ-E80qF_BVkjOe_wAyED0gdKgf8k394U&e=>
>
> LinkedIn: https://www.linkedin.com/in/travismack
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=0GDypIHm4hWEX5FJjFPfiiQwyZshxiZNeansIQGeBuE&s=tKwDQbYzBRk0qFZfVmqdixd9aKmd-gsjqW_oMvycbyU&e=>
>
>
>
> *“**The bitterness of poor quality remains long after the sweetness of
> low price is forgotten.”*
>
>
>
>
>
>
> ------------------------------
>
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
>
>
> ------------------------------
>
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
>
>
> ------------------------------
>
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org