There are a ton of specifics with FM and Ex Cov.  If you are not familiar,
you should likely spend a few hours reviewing 2-0, 3-0 and 3-26 before you
go down a rabbit hole and lose a ton of time.  Minimum spacings, minimum
pressures, minimum in design areas, etc.  There are a lot of things specific
to FM with these things.

 

I do believe you still follow the same 14x14, 16x16,e tc.but not 100%
positive without going back to review.

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:[email protected]> [email protected]

www.mfpdesign.com

 

Send large files to us via:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta
il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C
14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2
wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
https://www.hightail.com/u/MFPDesign 

LinkedIn:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked
in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%
7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L
sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
https://www.linkedin.com/in/travismack

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

 

 

From: Sprinklerforum <[email protected]> On
Behalf Of [email protected]
Sent: Thursday, July 11, 2019 10:01 AM
To: [email protected]
Subject: EC Heads in an FM Job

 

First off I've never used EC Sprinkler on an FM job, nor do I have much
experience with FM to begin with. 

 

I've always rounded up to the used the square spacing requirement from data
sheets i.e 14x14, 16x16  etc. when the sprinkler spacing was less than full
square. 

 

When in FM I would assume you do the same. But I've been told this is not
the case. I've read through some of the FM sheets an can't find where is
clearly say one way or the other. 

 

Can someone shed some light on this.  

 

 

Jerry Van Kolken

Millennium Fire Protection Corp.

2950 San Luis Rey Rd.

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 