This is just my opinion, but just because the definition doesn't reference 
motorcycle tires (or ATV tires for that matter, or the one on my wheel barrow) 
doesn't negate the fact that motorcycle tires are rubber tires. That definition 
doesn't comply with the NFPA Manual of Style either, so the definition is 
definitely flawed.

However, in Chapter 18 of NFPA 13-2013 (for example) tires on racks on tread 
are covered, so I don't think you really have a problem with design criteria.

Larry Keeping


From: Sprinklerforum <[email protected]> On Behalf 
Of David Bitton
Sent: July-12-19 4:34 PM
To: [email protected]
Subject: Storage of motorcycle tires

I am looking at a storage area for motorcycle tires on fixed racks on tread.  
NFPA 13 excludes such tires from its definition of rubber tires (FM 8-3 does 
not). I would like your opinion about how to determine protection criteria for 
this storage?  (Miscellaneous storage does not apply.)
Thanks,

David Bitton, ing./Eng.
Quest Loss Control Services Inc.
Les services de prévention des sinistres Quest
5100, rue de la Savane, bureau 200
Montréal, Québec
H4P 1T8
(514) 341-4545
www.questlosscontrol.com<http://www.questlosscontrol.com/>







_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to