Nope I think 6/12 top surface 4/12 lower..

David T Williams – Lead MEP/FP Engineer

LHB, Inc. | PERFORMANCE DRIVEN DESIGN.

From: Travis Mack <tm...@mfpdesign.com>
Sent: Thursday, August 15, 2019 2:40 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: b...@firebyknight.com; David Williams <david.willi...@lhbcorp.com>
Subject: Re: Attic/Concealed space access to sprinkler heads

What is your attic slope? Is <2:12 then you need specially listed sprinklers 
for the areas <36” deep.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Aug 15, 2019, at 12:02 PM, David Williams via Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:
Thanks.. I didn’t see it  either but I wanted to see if there were other 
opinions/options.

David T Williams – Lead MEP/FP Engineer

LHB, Inc. | PERFORMANCE DRIVEN DESIGN.

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Bob Knight via Sprinklerforum
Sent: Thursday, August 15, 2019 1:59 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Bob Knight <b...@firebyknight.com<mailto:b...@firebyknight.com>>
Subject: RE: Attic/Concealed space access to sprinkler heads

NFPA 25 does not require the inspection of sprinklers in concealed spaces, so 
that should not be an issue.


Thank you,

Bob Knight, CET III
Fire by Knight, LLC
208-318-3057

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of David Williams via Sprinklerforum
Sent: Thursday, August 15, 2019 12:43 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: David Williams
Subject: Attic/Concealed space access to sprinkler heads

I have a project intended to be fully sprinkled with a combustible attic that 
tapers from 2’ to 4 ‘ without being filled to within 2 inches of the deck with 
insulation. So I am planning on a dry pipe system with standard heads as the 
design of the attic does not allow the effective use of special application 
attic sprinklers.

The questions are: whether inspection access is required to be provided, is it 
prudent to do so at the heads, or can the locations just be noted on the gypsum 
mounted to the bottom chord of the open web trusses.

TIA

David T Williams, PE – Lead MEP/FP Engineer
21 West Superior Street, Suite 500, Duluth, MN 55802
Direct 218.279.2436 | Cell 218.310.2446
LHBcorp.com<http://www.LHBcorp.com>

LHB, Inc. | PERFORMANCE DRIVEN DESIGN.

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org