I have been asked to turn the valves so they don't protrude further from the wall than the standpipe does (leaving clearance for firefighter use) and run the standpipe down to the floor so the cane can find the bottom of the pipe. I have had an AHJ accept a piece of 1" that does from the bottom of the standpipe to the cap on the 4" to act as the detection. I don't think bollards would be required or at least they haven't been around here in North Carolina yet.
On Fri, Nov 22, 2019 at 12:40 PM Kyle.Montgomery via Sprinklerforum < [email protected]> wrote: > All, > > > > I’m running into some issues on a project where the AHJ is asking for > “Cane Detection”. For those of you who may not be familiar with the term, > the short answer is that cane detection is required for objects that > protrude into the circulation path so that a blind/visually impaired person > can detect the presence of the object with his/her cane and therefore not > bump into it. It’s required for objects that protrude more than 4” from the > wall, and are located within a height range of 27”-80”; objects higher than > 80” are above the required headroom clearance, and objects lower than 27” > are within the “cane sweep” and thus will be detected. (Just Google “Cane > Detection” for more information) > > > > I understand the need for this, but am uncertain of all the requirements. > Here’s our situation: > > > > We don’t need the detection for the standpipe itself (or the drain) > because that continues through the floor and can be detected by the cane. > However, the hose valves protrude more than 4” from the standpipe, and are > above 27”, so we’re being told that we need it for the hose valves. So, > I’ve got two questions: > > > > 1. Is the code being applied the correct way? Have any of you run > into this and are the any exceptions for standpipes or life safety > equipment? I’m wondering how this hasn’t been a problem for us many times > before if this is the correct interpretation of the code. > > 2. If this IS the correct requirement, should the installation of > cane detection fall to the fire sprinkler subcontractor? I mean, we’re not > typically responsible for installing bollards to protect risers in > warehouses and similar. > > > > I’m interested to hear the forum’s thoughts and experiences. Thanks for > your help. > > > > *Kyle Montgomery* > > [image: cid:[email protected]] > > *Aero Automatic Sprinkler Co.* > > *21605 N. Central Ave.* > > *Phoenix, AZ 85024* > > *Direct: 623.580.7820* > > *Cell: 602.763.4736* > > [email protected] > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Nick Maneen Estimator 2553 South Fayetteville Street Asheboro, NC 27205 P 336-625-2304 F 336-625-4649 C 704-791-7789
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org