I hope then when you combine what Ed Kramer and David Blackwell provided 
someone sees reason.

 


Nick Maneen, SET 

c 704.791.7789

 

From: Kyle.Montgomery [mailto:[email protected]] 
Sent: Friday, November 22, 2019 3:27 PM
To: Nick Maneen
Cc: [email protected]
Subject: RE: [EXTERNAL] Re: Cane Detection

 

Well, the building is 17 stories with two or more stairs on each level. So 
there’s over 40 hose valves. It will end up costing way more than a hundred 
bucks to satisfy the requirement they are proposing, regardless of the method 
we choose.

 

From: Nick Maneen [mailto:[email protected]] 
Sent: Friday, November 22, 2019 1:01 PM
To: Kyle.Montgomery <[email protected]>
Cc: [email protected]
Subject: RE: [EXTERNAL] Re: Cane Detection

 

I have only been asked to do something around standpipes in the last three 
years and both occasions they were in the path of egress.  It seems to me that 
if you are tucked into the corner and out of the way of normal travel, someone 
is being a little over zealous with their interpretation.  

 

As far as your next course of action, you have options.  I am all for fighting 
the fight and standing up for yourself that these valves are outside the path 
of egress, therefore the detection is not required.  Then if you discover you 
are talking to a wall, ask yourself if you would take a client out and spend 
$100 on dinner to secure future relationships and work?  Would you spend $100 
on this GC, roll your eyes at the inspector, and move on to the next project?  
My view on this is completely determined on the dollar amount spent.  I can 
think of all kinds of different scenarios where I would dig my heels in and not 
budge, but I don’t think this is one.  We recently gave a GC a case of 
escutcheons for free because the painter messed up the outer ring on dozens of 
heads and instead of going for the back charge to change them out, we went for 
the relationship.  

 


Nick Maneen, SET 

c 704.791.7789

 

From: Kyle.Montgomery [mailto:[email protected]] 
Sent: Friday, November 22, 2019 2:40 PM
To: Nick Maneen
Cc: [email protected]
Subject: RE: [EXTERNAL] Re: Cane Detection

 

Agreed, but the hose valve protrudes more than 4”. And unless we’re the only 
ones not privy to some kind of “micro hose valve” I’m pretty sure every 
standpipe installation in existence would have this same issue. Which is why 
I’m thinking there must be something I’m missing.

 

-Kyle M

 

From: Nick Maneen [mailto:[email protected]] 
Sent: Friday, November 22, 2019 12:36 PM
To: Kyle.Montgomery <[email protected]>
Cc: [email protected]
Subject: Re: [EXTERNAL] Re: Cane Detection

 

Sorry for the incomplete email.  It just went ahead and sent...

Anyway, in my experience, a piece of pipe on a floor flange under the standpipe 
should work.  It seems to follow the illustration David Blackwell sent.

 

On Fri, Nov 22, 2019 at 2:28 PM Kyle.Montgomery <[email protected]> 
wrote:

Nick, 

 

I wasn’t suggesting that bollards would be necessary, I was just comparing them 
as an example of something that may be required to go along with a 
sprinkler/standpipe system that typically would be provided “by others”. One of 
my issues right now is that the GC is siding with the AHJ and just saying “Yep, 
we need it, you need to provide it, no extra money.”

 

The problem we have is that the hose valves protrude more than 4” from the 
standpipe, so we’re being told it is required. But I’m pretty sure every hose 
valve on every standpipe in existence does this, so how has this never been an 
issue for us before?

 

-Kyle M

 

From: Nick Maneen [mailto:[email protected]] 
Sent: Friday, November 22, 2019 12:19 PM
To: [email protected]
Cc: Kyle.Montgomery <[email protected]>
Subject: [EXTERNAL] Re: Cane Detection

 

I have been asked to turn the valves so they don't protrude further from the 
wall than the standpipe does (leaving clearance for firefighter use) and run 
the standpipe down to the floor so the cane can find the bottom of the pipe.  I 
have had an AHJ accept a piece of 1" that does from the bottom of the standpipe 
to the cap on the 4" to act as the detection.  I don't think bollards would be 
required or at least they haven't been around here in North Carolina yet.  

 

On Fri, Nov 22, 2019 at 12:40 PM Kyle.Montgomery via Sprinklerforum 
<[email protected]> wrote:

All,

 

I’m running into some issues on a project where the AHJ is asking for “Cane 
Detection”. For those of you who may not be familiar with the term, the short 
answer is that cane detection is required for objects that protrude into the 
circulation path so that a blind/visually impaired person can detect the 
presence of the object with his/her cane and therefore not bump into it. It’s 
required for objects that protrude more than 4” from the wall, and are located 
within a height range of 27”-80”; objects higher than 80” are above the 
required headroom clearance, and objects lower than 27” are within the “cane 
sweep” and thus will be detected. (Just Google “Cane Detection” for more 
information)

 

I understand the need for this, but am uncertain of all the requirements. 
Here’s our situation:

 

We don’t need the detection for the standpipe itself (or the drain) because 
that continues through the floor and can be detected by the cane. However, the 
hose valves protrude more than 4” from the standpipe, and are above 27”, so 
we’re being told that we need it for the hose valves. So, I’ve got two 
questions:

 

1.       Is the code being applied the correct way? Have any of you run into 
this and are the any exceptions for standpipes or life safety equipment? I’m 
wondering how this hasn’t been a problem for us many times before if this is 
the correct interpretation of the code.

2.       If this IS the correct requirement, should the installation of cane 
detection fall to the fire sprinkler subcontractor? I mean, we’re not typically 
responsible for installing bollards to protect risers in warehouses and similar.

 

I’m interested to hear the forum’s thoughts and experiences. Thanks for your 
help.

 

Kyle Montgomery

 cid:[email protected]

Aero Automatic Sprinkler Co.

21605 N. Central Ave.

Phoenix, AZ 85024

Direct: 623.580.7820

Cell: 602.763.4736

[email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=ZbncDeKd4kt8sHgJUrCq0Fsv718COPm03mwxIoyBeCw&s=Yo7qU21orIb76JaDUEbO9Tvxv0-3PcDvVcQnXEh3S0w&e=>
 




 

-- 

Nick Maneen

Estimator

2553 South Fayetteville Street

Asheboro, NC 27205

P 336-625-2304

F 336-625-4649

C 704-791-7789




 

-- 

Nick Maneen

Estimator

2553 South Fayetteville Street

Asheboro, NC 27205

P 336-625-2304

F 336-625-4649

C 704-791-7789