I recently attended HROC (High Rise Operations Conference) in Pensacola on the invitation of two NFPA 14 committee members who are active fire service. It’s a fire service-only event and I was the only civilian in attendance – to say that I learned a lot is a great understatement as it was possibly the most informative professional event I’ve ever attended. Also, I got an earful from firefighters, captains and chiefs who regularly use standpipes in mid- and high-rise buildings.
The information in that card is VERY important to the engineer on the first due pumper. In fact, based on hearing about this from at least 8 or 9 different attendees at HROC, I’m going to introduce a committee input that would require that the inlet and outlet flow and pressure metrics be permanently labeled at each hose connection equipped with a pressure reducer. (On a side note, there is so much energy AGAINST factory-set PRV hose valves, you can’t imagine. Down to the last man and woman, firefighters want infinitely adjustable PRVs such as the Elkhart URFA and the new Zurn 5000 series.) Placing the basis of design on the documents is the first step and it enables enforcing the placement of the required signage at the inlet(s) and this information can literally shorten time-to-water by as much as 6-7 minutes by allowing the engineer to start pumping much closer to the target at the tip, regardless of whether the system has PRVs or not. I also agree with JD that format isn’t critical. SML From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Denhardt via Sprinklerforum Sent: Thursday, January 02, 2020 8:34 AM To: sprinklerforum@lists.firesprinkler.org Cc: John Denhardt; Travis Mack; Tom Wellen Subject: RE: SprinkCAD Standpipe Calculation Results on Installation Plans Agree. We show the information NFPA 14 requires. Format is not critical but the information must be shown. Thanks, John John August Denhardt, P.E. Strickland Fire Protection Incorporated 4011 Penn Belt Place Forestville, Maryland 20747-4737 301.474.1136 - Office 301.343.1457 - Mobile From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of Travis Mack via Sprinklerforum Sent: Thursday, January 2, 2020 11:31 AM To: sprinklerforum@lists.firesprinkler.org Cc: Travis Mack <tm...@mfpdesign.com>; Tom Wellen <tgwel...@gmail.com> Subject: Re: SprinkCAD Standpipe Calculation Results on Installation Plans We always show that exact sign indicated in A6.8 on the plans. Travis Mack, CFPS, CWBSP, RME-G, SET 480-505-9271 x700 MFP Design, LLC www.mfpdesign,com<http://www.mfpdesign,com> Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone On Jan 2, 2020, at 9:25 AM, Tom Wellen via Sprinklerforum <sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>> wrote: I requested that standpipe design information from calculations be provided on the plans per 6.8 and Figure A.6.8 of NFPA 14. The contractor indicated that SprinkCAD provide a standardized hydraulic result. That seems like a lame response. I'm sure another format or even text information could be provided rather than using NFPA 13's Hydraulic Calculation results for the design area. What do you provide the required information from 6.8? Tom Wellen _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org