Could it be related to seismic movement of unrestrained ductwork against the FP 
pipe?

When you say ductwork, is that ½” between pipe and insulation or actual sheet 
metal?

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 8:54 AM
To: 
<[email protected]<mailto:[email protected]>>
 
<[email protected]<mailto:[email protected]>>
Cc: Travis Mack <[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] Pipe adjacent to duct

We have a project where the fire inspector is stating that the fire sprinkler 
main is too close to ductwork.  There is a 6” main that is about 1/2” from the 
ductwork.

Of course, the inspectors response is “it’s in the code book” when asking for a 
reference that mandates clearance to hvac ductwork.

Has anyone run into something similar?

Note: this is not a high temp duct that would cause for enough heat to convert 
the sprinkler water to steam. This is just your standard, run of the mill, HVAC 
system.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271 x700
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign<https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!VcjF30iEaFuEx1cvHWPEx0GwlCXjsi62_q06GNj_cf6hxAEmmhx_JZyYbSEuPjBOcw$>

Sent from my iPhone

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to