Travis,

The only thing I can think of is where there is to be a 2” clearance to 
structural that isn’t supporting piping.  The AHJ could be confused as to what 
is structural and what isn’t.

 

 

Thank you,

 

Bob Knight, CET III

Fire by Knight, LLC

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 6:54 AM
To: <[email protected]>
Cc: Travis Mack
Subject: Pipe adjacent to duct

 

We have a project where the fire inspector is stating that the fire sprinkler 
main is too close to ductwork.  There is a 6” main that is about 1/2” from the 
ductwork. 

 

Of course, the inspectors response is “it’s in the code book” when asking for a 
reference that mandates clearance to hvac ductwork. 

 

Has anyone run into something similar?

 

Note: this is not a high temp duct that would cause for enough heat to convert 
the sprinkler water to steam. This is just your standard, run of the mill, HVAC 
system. 