The only reference to clearance is for structural members
NFPA 13 – 2016 edition: 9.3.4.9 The installed horizontal and upward vertical clearance between horizontal sprinkler piping and structural members not penetrated or used, collectively or independently, to support the piping shall be at least 2 in. (50 mm). If it were a branch-line with sprinklers then per NFPA 13 -2016 edition: 9.3.4.11* The installed clearance between a sprinkler and structural elements not used collectively or independently to support the sprinklers shall be at least 3 in. (75 mm). Nothing referencing Mechanical that I know of. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office: 253-872-7222 <https://archerconstruction.com/> https://archerconstruction.com From: Prahl, Craig/GVL <[email protected]> Sent: Wednesday, January 15, 2020 8:54 AM To: [email protected] Cc: Travis Mack, SET, CFPS, CWBSP, RME-G <[email protected]> Subject: RE: [EXTERNAL] Pipe adjacent to duct Well, when I’ve gotten that “it’s in the code” response from an AHJ and I am pretty certain it is not, I respectfully request them to please provide me with the code reference so I can present it as part of my Change Notice to the GC for design modifications which cannot be made until such code reference is received and the change is approved. This way I’m not challenging them, but seeking their assistance. When they can’t produce any reference, the issue goes away. I copy key people on the project so that they are aware of the issue. It’s just a more diplomatic way of saying “prove it”. The fact is that most AHJ types or reviewers only review the drawings associated with their specific area of responsibility. They do not care about coordination, that’s part of the responsibility of the design professional. So they would most likely never pick up on something like this during permit reviews. Ain’t this fun? “I need you to move your 8” system main, I’ve got a ½” water line that needs to get through.” Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | <mailto:[email protected]> [email protected] | <http://www.jacobs.com/> www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 From: Sprinklerforum <[email protected] <mailto:[email protected]> > On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum Sent: Wednesday, January 15, 2020 11:44 AM To: [email protected] <mailto:[email protected]> Cc: Travis Mack, SET, CFPS, CWBSP, RME-G <[email protected] <mailto:[email protected]> > Subject: RE: [EXTERNAL] Pipe adjacent to duct Exactly. It’s all up in the air. It was a BIM job and not an issue with anyone during coordination. Now it’s all up in the air installed and seems to be an issue. You can’t win some days. Plus, it shouldn’t be an issue at all, but now it is. <https://urldefense.com/v3/__http:/www.mfpdesign.com/__;!!B5cixuoO7ltTeg!SYGlq52zxPFHvfw4LVunwooDhKL-TrLct9Q-XaSad4uj6L61mxK7neezT8XzAYnzSg$> Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 NEW EXTENSION: 480-505-9271 ext. 700 fax: 866-430-6107 <mailto:[email protected]> [email protected] www.mfpdesign.com <https://urldefense.com/v3/__http:/www.mfpdesign.com__;!!B5cixuoO7ltTeg!SYGlq52zxPFHvfw4LVunwooDhKL-TrLct9Q-XaSad4uj6L61mxK7neezT8WzVSu4mQ$> Send large files to us via: <https://urldefense.com/v3/__https:/na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.hightail.com*2Fu*2FMFPDesign&data=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5*2BAZvlHhABSexWY*3D&reserved=0__;JSUlJSUlJSUlJSUlJSU!!B5cixuoO7ltTeg!SYGlq52zxPFHvfw4LVunwooDhKL-TrLct9Q-XaSad4uj6L61mxK7neezT8VaBc3Www$> https://www.hightail.com/u/MFPDesign LinkedIn: <https://urldefense.com/v3/__https:/na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.linkedin.com*2Fin*2Ftravismack&data=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN*2BZodi*2FhbeCbHNRijI*3D&reserved=0__;JSUlJSUlJSUlJSUlJSUl!!B5cixuoO7ltTeg!SYGlq52zxPFHvfw4LVunwooDhKL-TrLct9Q-XaSad4uj6L61mxK7neezT8XHIcau2Q$> https://www.linkedin.com/in/travismack “The bitterness of poor quality remains long after the sweetness of low price is forgotten.” From: Sprinklerforum <[email protected] <mailto:[email protected]> > On Behalf Of Prahl, Craig/GVL via Sprinklerforum Sent: Wednesday, January 15, 2020 9:41 AM To: [email protected] <mailto:[email protected]> Cc: Prahl, Craig/GVL <[email protected] <mailto:[email protected]> >; Travis Mack <[email protected] <mailto:[email protected]> >; David Bohannon <[email protected] <mailto:[email protected]> >; Matthew J Willis <[email protected] <mailto:[email protected]> >; [email protected] <mailto:[email protected]> Subject: RE: [EXTERNAL] Pipe adjacent to duct Well it’s only a click of the mouse and it’s moved, so what’s your problem? 😉 Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | <mailto:[email protected]> [email protected] | <http://www.jacobs.com/> www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 From: Sprinklerforum <[email protected] <mailto:[email protected]> > On Behalf Of Travis Mack via Sprinklerforum Sent: Wednesday, January 15, 2020 11:34 AM To: [email protected] <mailto:[email protected]> Cc: Travis Mack <[email protected] <mailto:[email protected]> >; [email protected] <mailto:[email protected]> ; Matthew J Willis <[email protected] <mailto:[email protected]> >; David Bohannon <[email protected] <mailto:[email protected]> > Subject: Re: [EXTERNAL] Pipe adjacent to duct Lol. That’s too funny. Everyone thinks fire sprinkler can just magically move. Travis Mack, CFPS, CWBSP, RME-G, SET 480-505-9271 x700 MFP Design, LLC www.mfpdesign,com <https://urldefense.com/v3/__http:/www.mfpdesign,com__;!!B5cixuoO7ltTeg!SYGlq52zxPFHvfw4LVunwooDhKL-TrLct9Q-XaSad4uj6L61mxK7neezT8VAMQ0gjA$> Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign <https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona4GLVqxWQ$> Sent from my iPhone On Jan 15, 2020, at 9:23 AM, Matthew J Willis via Sprinklerforum <[email protected] <mailto:[email protected]> > wrote: Hahahahaha From: David Bohannon <[email protected] <mailto:[email protected]> > Sent: Wednesday, January 15, 2020 9:21 AM To: [email protected] <mailto:[email protected]> Cc: Matthew J Willis <[email protected] <mailto:[email protected]> >; [email protected] <mailto:[email protected]> Subject: RE: [EXTERNAL] Pipe adjacent to duct Just a question. If the duct is to close to the fire main why wouldn’t the duct have to move? Isn’t life safety more important than climate comfort? Sent from AOL Mobile Mail Get the new AOL app: mail.mobile.aol.com <https://urldefense.com/v3/__http:/mail.mobile.aol.com__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7NH3VpRw$> On Wednesday, January 15, 2020, John Denhardt via Sprinklerforum <[email protected] <mailto:[email protected]> > wrote: I am unaware of any language that would support the fire inspector’s position. Thanks, John John August Denhardt, P.E. Vice President Engineering and Technical Services American Fire Sprinkler Association 301.343.1457 - Mobile From: Sprinklerforum <[email protected] <mailto:[email protected]> > On Behalf Of Matthew J Willis via Sprinklerforum Sent: Wednesday, January 15, 2020 10:00 AM To: [email protected] <mailto:[email protected]> Cc: Matthew J Willis <[email protected] <mailto:[email protected]> > Subject: RE: [EXTERNAL] Pipe adjacent to duct Educate him. Use your charm. R/ Matt From: Sprinklerforum <[email protected] <mailto:[email protected]> > On Behalf Of Travis Mack via Sprinklerforum Sent: Wednesday, January 15, 2020 7:16 AM To: [email protected] <mailto:[email protected]> Cc: Travis Mack <[email protected] <mailto:[email protected]> >; Prahl, Craig/GVL <[email protected] <mailto:[email protected]> > Subject: Re: [EXTERNAL] Pipe adjacent to duct No seismic. No insulation. Travis Mack, CFPS, CWBSP, RME-G, SET 480-505-9271 x700 MFP Design, LLC www.mfpdesign,com <https://urldefense.com/v3/__http:/www.mfpdesign,com__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7aUKCG7Q$> Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign <https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona4GLVqxWQ$> Sent from my iPhone On Jan 15, 2020, at 7:12 AM, Prahl, Craig/GVL via Sprinklerforum <[email protected] <mailto:[email protected]> > wrote: Could it be related to seismic movement of unrestrained ductwork against the FP pipe? When you say ductwork, is that ½” between pipe and insulation or actual sheet metal? Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | <mailto:[email protected]> [email protected] | <http://www.jacobs.com/> www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 From: Sprinklerforum <[email protected] <mailto:[email protected]> > On Behalf Of Travis Mack via Sprinklerforum Sent: Wednesday, January 15, 2020 8:54 AM To: <[email protected] <mailto:[email protected]> > <[email protected] <mailto:[email protected]> > Cc: Travis Mack <[email protected] <mailto:[email protected]> > Subject: [EXTERNAL] Pipe adjacent to duct We have a project where the fire inspector is stating that the fire sprinkler main is too close to ductwork. There is a 6” main that is about 1/2” from the ductwork. Of course, the inspectors response is “it’s in the code book” when asking for a reference that mandates clearance to hvac ductwork. Has anyone run into something similar? Note: this is not a high temp duct that would cause for enough heat to convert the sprinkler water to steam. This is just your standard, run of the mill, HVAC system. Travis Mack, CFPS, CWBSP, RME-G, SET 480-505-9271 x700 MFP Design, LLC www.mfpdesign,com <https://urldefense.com/v3/__http:/www.mfpdesign,com__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7aUKCG7Q$> Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign <https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!VcjF30iEaFuEx1cvHWPEx0GwlCXjsi62_q06GNj_cf6hxAEmmhx_JZyYbSEuPjBOcw$> Sent from my iPhone _____ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer. _______________________________________________ Sprinklerforum mailing list [email protected] <mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org <https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7JwYI3NA$> _______________________________________________ Sprinklerforum mailing list [email protected] <mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org <https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7JwYI3NA$> _______________________________________________ Sprinklerforum mailing list [email protected] <mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org <https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7JwYI3NA$> _____ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer. _____ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org