NFPA 13 2016 Edition

7.7.6 Strainers. A listed strainer shall be provided in the riser
or feed main that supplies sprinklers having nominal K-factors
smaller than K-2.8 (40).

On Mon, Feb 3, 2020 at 1:40 PM Steve Leyton via Sprinklerforum <
[email protected]> wrote:

> More specifically, backflows are not fire protection devices, which is why
> they are not prescribed by the sprinkler standard.   The local health and
> water departments are the enforcing agencies with regard to backflow
> prevention and cross-connection control, and generally speaking a backflow
> appliance is only required to be installed on a private connection to the
> public water system that will supply a non-potable demand.  So in 99+% of
> scenarios, the installation of a strainer would be governed by the serving
> water agency since it occurs on the public side (and often in the public
> right-of-way) of the backflow appliance.   Questions you have about such
> equipment should be directed to the cross-connection control department of
> the water purveyor.
>
>
>
> Steve Leyton
>
>
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Matthew J
> Willis via Sprinklerforum
> *Sent:* Monday, February 03, 2020 11:36 AM
> *To:* [email protected]
> *Cc:* Matthew J Willis
> *Subject:* RE: Strainers On the Backflow
>
>
>
> Backflows, technically, are really not part of 13.
>
>
>
> They are included in-so-far as municipalities dictate them.
>
>
>
> Therefore, the data sheet is the only real refuge for the info.
>
>
>
> As per yours below, do not use a strainer on our systems.
>
>
>
> R/
>
> Matt
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *Michael Goodis via Sprinklerforum
> *Sent:* Monday, February 3, 2020 12:06 PM
> *To:* [email protected]
> *Cc:* Michael Goodis <[email protected]>
> *Subject:* Strainers On the Backflow
>
>
>
> Guys,
>
>
>
> I am looking and cant seem to find any info on strainers that are
> installed on a fire protection line in front of the fire backflow.  I found
> on the backflow submittal where it states it, but is it in NFPA 13 and
> possibly UFC 03-600-01?
>
>
>
>
>
> Thanks,
>
>
>
> *Michael Goodis     *
>
> *Salesman, Project Manager*
>
> *IL#000635   NICET#135586*
>
> *Key Fire Protection Enterprises LLC*
>
> *3200 Mike Padgett HWY*
>
> *Augusta, GA 30906*
>
> *Office- (706) 790-3473*
>
> *Cell- (706) 220-8822*
>
> *Fax: (706) 738-2119*
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to