Sure, but that can be on the private side of any backflow. From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jeff Normand via Sprinklerforum Sent: Monday, February 03, 2020 12:15 PM To: [email protected] Cc: Jeff Normand Subject: Re: Strainers On the Backflow
NFPA 13 2016 Edition 7.7.6 Strainers. A listed strainer shall be provided in the riser or feed main that supplies sprinklers having nominal K-factors smaller than K-2.8 (40). On Mon, Feb 3, 2020 at 1:40 PM Steve Leyton via Sprinklerforum <[email protected]<mailto:[email protected]>> wrote: More specifically, backflows are not fire protection devices, which is why they are not prescribed by the sprinkler standard. The local health and water departments are the enforcing agencies with regard to backflow prevention and cross-connection control, and generally speaking a backflow appliance is only required to be installed on a private connection to the public water system that will supply a non-potable demand. So in 99+% of scenarios, the installation of a strainer would be governed by the serving water agency since it occurs on the public side (and often in the public right-of-way) of the backflow appliance. Questions you have about such equipment should be directed to the cross-connection control department of the water purveyor. Steve Leyton From: Sprinklerforum [mailto:[email protected]<mailto:[email protected]>] On Behalf Of Matthew J Willis via Sprinklerforum Sent: Monday, February 03, 2020 11:36 AM To: [email protected]<mailto:[email protected]> Cc: Matthew J Willis Subject: RE: Strainers On the Backflow Backflows, technically, are really not part of 13. They are included in-so-far as municipalities dictate them. Therefore, the data sheet is the only real refuge for the info. As per yours below, do not use a strainer on our systems. R/ Matt From: Sprinklerforum <[email protected]<mailto:[email protected]>> On Behalf Of Michael Goodis via Sprinklerforum Sent: Monday, February 3, 2020 12:06 PM To: [email protected]<mailto:[email protected]> Cc: Michael Goodis <[email protected]<mailto:[email protected]>> Subject: Strainers On the Backflow Guys, I am looking and cant seem to find any info on strainers that are installed on a fire protection line in front of the fire backflow. I found on the backflow submittal where it states it, but is it in NFPA 13 and possibly UFC 03-600-01? [cid:[email protected]] Thanks, Michael Goodis Salesman, Project Manager IL#000635 NICET#135586 Key Fire Protection Enterprises LLC 3200 Mike Padgett HWY Augusta, GA 30906 Office- (706) 790-3473 Cell- (706) 220-8822 Fax: (706) 738-2119 _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org