My thoughts - cooking oil is a class IIIB combustible liquid; the model 
building codes would limit to not more than 13,200 gallons before changing to 
an H use group.  If the containers are metal, then no issue.  If they are 
plastic (prohibited for class I flammables and class II and IIIA combustible 
liquids), then more consideration should be given to density, particularly if 
the containers were to remain exposed/unprotected from persons or adjacent 
vehicles (think car fire exposure, etc.).

Andrew Steele




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Sean Lockyer via Sprinklerforum
Sent: Wednesday, February 26, 2020 9:38 AM
To: Prahl, Craig/GVL; [email protected]
Cc: Sean Lockyer
Subject: RE: Flammable liquid tanks in a garage

Craig,
        Cooking oils are being stored; per the specs I was provided the tanks 
meet the requirements of NFPA 30 (2015) and Chapter 19.7 of the 2015 IFC. As 
for the existing system, the garage was designed for an ordinary group 1 and is 
protected with a dry system. The initial fear from my service side was that 
this would require the system to be re-calculated for an extra hazard (and 
thus, completely reworked based upon the density).

My hope is that an enclosure in accordance with NFPA would be sufficient but I 
am still trying to gather more information before I approach the AHJ.

Hope this helps. Thanks for all of the ideas so far...

-Sean
        

-----Original Message-----
From: Prahl, Craig/GVL <[email protected]> 
Sent: Wednesday, February 26, 2020 9:21 AM
To: [email protected]
Cc: Sean Lockyer <[email protected]>
Subject: RE: Flammable liquid tanks in a garage

What kind of flammable liquid would be used in a restaurant?  Liquid propane?

And you say the garage area has sprinkler protection?  What density?  Wet or 
dry?

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
[email protected] | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Sean Lockyer via Sprinklerforum
Sent: Wednesday, February 26, 2020 12:29 AM
To: [email protected]
Cc: Sean Lockyer <[email protected]>; 
[email protected]
Subject: [EXTERNAL] Flammable liquid tanks in a garage

There is a garage with an existing system that has a restaurant on the floor 
above; the restaurant has (2) exposed flammable liquid tanks in the garage 
(with piping connected from the restaurant above to the tanks below. Question: 
What does this do to the hazard classification in the garage ? Would the owner 
need to built an NFPA 30 type enclosure around the tanks ? A bit of a grey area 
and not really sure how to proceed. Never seen this before. What says everyone ?


            Sean Lockyer
            Project Designer                               6817 N. Orange 
Blossom Trail
            Cell    386-279-1197                             Orlando, Florida 
32810
            [email protected]             Phone:    407-816-9101
            www.AITLifeSafety.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!QIHpVwEkXI3H-6EHVx-DUOsN7fOS8TV-3xeDn8VOukm2Ctiy-Jo_Cn-CsdzalvTnbg$

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to