But not the treads, and it's almost certainly not Type 'X' gyp board, right?   
Splitting hairs over limited combustibility when there's exposed wood in any 
compartment isn't usually a fruitful exchange with most fire officials and 
based on your description, my first instinct is that these should be 
sprinklered per the prescription in 13, i.e. sprinklers at both sets of 
landings.

SL

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of tstone52--- via Sprinklerforum
Sent: Friday, July 24, 2020 10:21 AM
To: [email protected]
Cc: [email protected]
Subject: RE: Combustible Stairs

Yes. Wood Framed with wood treads. 
All the framing is covered by Sheetrock.

Regards,
G. Tim Stone
 
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
 
   117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968
             [email protected]

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Fpdcdesign via Sprinklerforum
Sent: Friday, July 24, 2020 12:45 PM
To: Sprinklerforum <[email protected]>
Cc: Fpdcdesign <[email protected]>
Subject: Re: Combustible Stairs

     
 

 Are the stairs wood?
 

 
 

 
 
>  
> On Jul 24, 2020 at 12:43 PM,  <tstone52--- via Sprinklerforum
(mailto:[email protected])>  wrote:
>  
>  
>  
>  Is Sprinkler Protection required under intermediate landings of
Combustible Construction Stairways even though all finished surfaces are to be 
Sheetrocked, (Limited Combustible material). I reference NFPA 13, 2013 ed., 
Chapter 8.15.3.1 Combustible Construction "Stairways". Thank you in advance. 
Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering 
Technician Fire Protection Sprinkler Design and Consulting Services 117 Old 
Stage Rd. - Essex Jct., VT. 05452 CELL: (802) 373-0638 TEL:
(802) 434-2968  <mailto:[email protected]>  [email protected] 
_______________________________________________ Sprinklerforum mailing list 
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

>
>  
 
 
     
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to