I agree with Steve's reasoning. However, the wording of A.8.15.3.2.1 "Sprinklers at each floor level landing should be positioned to protect both the floor level landing and any intermediate landing." leads me to believe it's not the intent to install sprinklers beneath intermediate landings (except the lowest one per 8.15.3.1.3).
Ed K -----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Steve Leyton via Sprinklerforum Sent: Friday, July 24, 2020 12:41 PM To: [email protected] Cc: Steve Leyton <[email protected]>; [email protected] Subject: RE: Combustible Stairs But not the treads, and it's almost certainly not Type 'X' gyp board, right? Splitting hairs over limited combustibility when there's exposed wood in any compartment isn't usually a fruitful exchange with most fire officials and based on your description, my first instinct is that these should be sprinklered per the prescription in 13, i.e. sprinklers at both sets of landings. SL -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of tstone52--- via Sprinklerforum Sent: Friday, July 24, 2020 10:21 AM To: [email protected] Cc: [email protected] Subject: RE: Combustible Stairs Yes. Wood Framed with wood treads. All the framing is covered by Sheetrock. Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd. - Essex Jct., VT. 05452 CELL: (802) 373-0638 TEL: (802) 434-2968 [email protected] -----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Fpdcdesign via Sprinklerforum Sent: Friday, July 24, 2020 12:45 PM To: Sprinklerforum <[email protected]> Cc: Fpdcdesign <[email protected]> Subject: Re: Combustible Stairs Are the stairs wood? > > On Jul 24, 2020 at 12:43 PM, <tstone52--- via Sprinklerforum (mailto:[email protected])> wrote: > > > > Is Sprinkler Protection required under intermediate landings of Combustible Construction Stairways even though all finished surfaces are to be Sheetrocked, (Limited Combustible material). I reference NFPA 13, 2013 ed., Chapter 8.15.3.1 Combustible Construction "Stairways". Thank you in advance. Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd. - Essex Jct., VT. 05452 CELL: (802) 373-0638 TEL: (802) 434-2968 <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org