Brian, I may be looking at this too 'simply', but wouldnt your suction pressure be the static pressure at the flow test location plus or minus any pressure gain or loss for any difference between the elevation of the flow test and the fire pump suction?
Cliff Whitfield, SET President Fire Design, Inc. 600 W. Bypass Hwy. 19E Suite 202 Burnsville, NC 28714 Ph: 828-284-4772 -----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Brian Harris via Sprinklerforum Sent: Thursday, August 6, 2020 11:24 AM To: [email protected] Cc: Brian Harris <[email protected]> Subject: Pump Suction Pressure (NPSH) We're replacing a pump in an existing system and the pump vendor wants to know the pump suction pressure. Since we didn't do the original system and I know nothing about it what is a practical way of determining the pump suction to tell the vendor? Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -- This email has been checked for viruses by Avast antivirus software. https://www.avast.com/antivirus _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org