360 psi to 725 psi. All threaded connections, no grooved stuff allowed. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | [email protected] | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606
-----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Shawn Foor via Sprinklerforum Sent: Monday, August 17, 2020 1:10 PM To: sprinklerforum <[email protected]> Cc: Shawn Foor <[email protected]>; Jeff Normand <[email protected]> Subject: [EXTERNAL] Re: Flexible assembly for Novec 1230 at seismic separation joint What kind of pressure are you talking about? I think the fireloop is only rated to 300 psi On Mon, Aug 17, 2020 at 11:10 AM Jeff Normand via Sprinklerforum < [email protected]> wrote: > https://urldefense.com/v3/__http://www.metrafire.com/fireloop/__;!!B5c > ixuoO7ltTeg!WZG5MkOV6Va5jK1MtaVL2bT5FK8yzOZiAJ3Hj0KNWBzXojSinZlyavpwau > a8Ngz5PQ$ > > Think they can be mounted horizontally and vertically. > > On Mon, Aug 17, 2020 at 10:44 AM Prahl, Craig/GVL via Sprinklerforum < > [email protected]> wrote: > > > Has anyone had to provide a flexible assembly on a NOVEC 1230 system > where > > the piping has to pass through a seismic separation joint? > > > > Looking for options. Architect gave us no space for cylinders in > > the rooms, contractor says they can't make it happen. > > > > Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | > > 864.676.5252 | [email protected] | http://www.jacobs.com > > 1041 East Butler Road Greenville, South Carolina 29606 > > > > > > ________________________________ > > > > NOTICE - This communication may contain confidential and privileged > > information that is for the sole use of the intended recipient. Any > > viewing, copying or distribution of, or reliance on this message by > > unintended recipients is strictly prohibited. If you have received > > this message in error, please notify us immediately by replying to > > the message and deleting it from your computer. > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > > > > https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cg > i/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!WZG5MkOV6Va5jK1M > taVL2bT5FK8yzOZiAJ3Hj0KNWBzXojSinZlyavpwauawd5vbug$ > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cg > i/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!WZG5MkOV6Va5jK1M > taVL2bT5FK8yzOZiAJ3Hj0KNWBzXojSinZlyavpwauawd5vbug$ > -- Shawn Foor, SET *FOOR DESIGN, LLC* *10208 E 98TH ST* *TULSA, OK 74133* *P:918-237-1400* _______________________________________________ Sprinklerforum mailing list [email protected] https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!WZG5MkOV6Va5jK1MtaVL2bT5FK8yzOZiAJ3Hj0KNWBzXojSinZlyavpwauawd5vbug$ ________________________________ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org