They may be referencing the International Fire Code.  The section is vague on 
the equipment access distance, so I have seen some use 36" because it used for 
clearance around hydrants and FDCs.  

509.2 Equipment access. Approved access shall be provided
and maintained for all fire protection equipment to permit
immediate safe operation and maintenance of such equipment.
Storage, trash and other materials or objects shall not
be placed or kept in such a manner that would prevent such
equipment from being readily accessible.

507.5.5 Clear space around hydrants. A 3-foot (914
mm) clear space shall be maintained around the circumference
of fire hydrants, except as otherwise required or
approved.

912.4.2 Clear space around connections. A working
space of not less than 36 inches (914 mm) in width, 36
inches (914 mm) in depth and 78 inches (1981 mm) in
height shall be provided and maintained in front of and to
the sides of wall-mounted fire department connections and
around the circumference of free-standing fire department
connections, except as otherwise required or approved by
the fire code official.

-----Original Message----- 
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Taylor Schumacher via Sprinklerforum
Sent: Thursday, November 5, 2020 2:01 PM
To: [email protected]
Cc: Taylor Schumacher <[email protected]>
Subject: RE: Clearance around all pump equipment

Check with local amendments to the code, I have seen some have 36" in front of 
the pump or riser assembly only and some have 36" all sides.


Taylor Schumacher




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton via Sprinklerforum
Sent: Thursday, November 05, 2020 3:47 PM
To: [email protected]
Cc: Steve Leyton; [email protected]
Subject: RE: Clearance around all pump equipment

I'm only aware of prescriptive clearance requirements in front of controller 
doors, which is per the NEC as Matthew cited.   We've NEVER programmed a 3' 
clearance around mechanical equipment.

Steve L.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack via Sprinklerforum
Sent: Thursday, November 05, 2020 1:39 PM
To: [email protected]
Cc: [email protected]
Subject: Clearance around all pump equipment

Is there anything in any fire code or standard that requires a 3' clearance 
around ALL pump room equipment.  We are maintaining 3' clear of controllers.  
It is being brought up he wants 3' clear of everything.  We asked for a 
reference.  The response was "in the book."

Any help or guidance?


Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
[email protected]
www.mfpdesign.com

Send large files to us via: 
https://urldefense.proofpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign&d=DwIGaQ&c=jVj56eFZMBdw2XTy1WmujjlEfwGR4yGcPx8hs15Otm8&r=SqEE8dddEcFzYmSZdqK2NnlRtkrj2jI_1dLmK8Yaacg&m=iuTtMGmiC9yV3rl1fyKeu2DVYym7MtYKBqjGuiv5GZE&s=LKot-63MfZ_jSoCgRVH2RabjVZmX5_gG9bGQVKLqszw&e=
 
LinkedIn: 
https://urldefense.proofpoint.com/v2/url?u=https-3A__www.linkedin.com_in_travismack&d=DwIGaQ&c=jVj56eFZMBdw2XTy1WmujjlEfwGR4yGcPx8hs15Otm8&r=SqEE8dddEcFzYmSZdqK2NnlRtkrj2jI_1dLmK8Yaacg&m=iuTtMGmiC9yV3rl1fyKeu2DVYym7MtYKBqjGuiv5GZE&s=llZ9Uk3zZfIapaftM6mk_CDP4uRQfUOtZQhKtgjURWc&e=
 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

Need/Want a faster way to check material pricing?  Build a material quote?  
Check availability ?   Searching for an invoice?
*If you do not already have an account with ferguson.com, click here to 
register.* **Have a Ferguson account? Download the Ferguson app for on-the-go 
access to your favorite ferguson.com features. Apple iOS devices or Android 
devices**

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=jVj56eFZMBdw2XTy1WmujjlEfwGR4yGcPx8hs15Otm8&r=SqEE8dddEcFzYmSZdqK2NnlRtkrj2jI_1dLmK8Yaacg&m=iuTtMGmiC9yV3rl1fyKeu2DVYym7MtYKBqjGuiv5GZE&s=2tSlfGc5F-IP8q1UYRidxg_4QvrztY_q70OY5_HSSAM&e=
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=jVj56eFZMBdw2XTy1WmujjlEfwGR4yGcPx8hs15Otm8&r=SqEE8dddEcFzYmSZdqK2NnlRtkrj2jI_1dLmK8Yaacg&m=iuTtMGmiC9yV3rl1fyKeu2DVYym7MtYKBqjGuiv5GZE&s=2tSlfGc5F-IP8q1UYRidxg_4QvrztY_q70OY5_HSSAM&e=
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=jVj56eFZMBdw2XTy1WmujjlEfwGR4yGcPx8hs15Otm8&r=SqEE8dddEcFzYmSZdqK2NnlRtkrj2jI_1dLmK8Yaacg&m=iuTtMGmiC9yV3rl1fyKeu2DVYym7MtYKBqjGuiv5GZE&s=2tSlfGc5F-IP8q1UYRidxg_4QvrztY_q70OY5_HSSAM&e=
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to