They may be referencing the International Fire Code. The section is vague on the equipment access distance, so I have seen some use 36" because it used for clearance around hydrants and FDCs.
509.2 Equipment access. Approved access shall be provided and maintained for all fire protection equipment to permit immediate safe operation and maintenance of such equipment. Storage, trash and other materials or objects shall not be placed or kept in such a manner that would prevent such equipment from being readily accessible. 507.5.5 Clear space around hydrants. A 3-foot (914 mm) clear space shall be maintained around the circumference of fire hydrants, except as otherwise required or approved. 912.4.2 Clear space around connections. A working space of not less than 36 inches (914 mm) in width, 36 inches (914 mm) in depth and 78 inches (1981 mm) in height shall be provided and maintained in front of and to the sides of wall-mounted fire department connections and around the circumference of free-standing fire department connections, except as otherwise required or approved by the fire code official. -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Taylor Schumacher via Sprinklerforum Sent: Thursday, November 5, 2020 2:01 PM To: [email protected] Cc: Taylor Schumacher <[email protected]> Subject: RE: Clearance around all pump equipment Check with local amendments to the code, I have seen some have 36" in front of the pump or riser assembly only and some have 36" all sides. Taylor Schumacher -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Steve Leyton via Sprinklerforum Sent: Thursday, November 05, 2020 3:47 PM To: [email protected] Cc: Steve Leyton; [email protected] Subject: RE: Clearance around all pump equipment I'm only aware of prescriptive clearance requirements in front of controller doors, which is per the NEC as Matthew cited. We've NEVER programmed a 3' clearance around mechanical equipment. Steve L. -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack via Sprinklerforum Sent: Thursday, November 05, 2020 1:39 PM To: [email protected] Cc: [email protected] Subject: Clearance around all pump equipment Is there anything in any fire code or standard that requires a 3' clearance around ALL pump room equipment. We are maintaining 3' clear of controllers. It is being brought up he wants 3' clear of everything. We asked for a reference. The response was "in the book." Any help or guidance? Travis Mack, CFPS, CWBSP, RME-G, SET Engineering Manager MFP Design 3356 E Vallejo Ct Gilbert, AZ 85298 NEW EXTENSION: 480-505-9271 ext. 700 NEW MOBILE: 480-272-2471 [email protected] www.mfpdesign.com Send large files to us via: https://urldefense.proofpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign&d=DwIGaQ&c=jVj56eFZMBdw2XTy1WmujjlEfwGR4yGcPx8hs15Otm8&r=SqEE8dddEcFzYmSZdqK2NnlRtkrj2jI_1dLmK8Yaacg&m=iuTtMGmiC9yV3rl1fyKeu2DVYym7MtYKBqjGuiv5GZE&s=LKot-63MfZ_jSoCgRVH2RabjVZmX5_gG9bGQVKLqszw&e= LinkedIn: https://urldefense.proofpoint.com/v2/url?u=https-3A__www.linkedin.com_in_travismack&d=DwIGaQ&c=jVj56eFZMBdw2XTy1WmujjlEfwGR4yGcPx8hs15Otm8&r=SqEE8dddEcFzYmSZdqK2NnlRtkrj2jI_1dLmK8Yaacg&m=iuTtMGmiC9yV3rl1fyKeu2DVYym7MtYKBqjGuiv5GZE&s=llZ9Uk3zZfIapaftM6mk_CDP4uRQfUOtZQhKtgjURWc&e= “The bitterness of poor quality remains long after the sweetness of low price is forgotten.” Need/Want a faster way to check material pricing? Build a material quote? Check availability ? Searching for an invoice? *If you do not already have an account with ferguson.com, click here to register.* **Have a Ferguson account? Download the Ferguson app for on-the-go access to your favorite ferguson.com features. Apple iOS devices or Android devices** _______________________________________________ Sprinklerforum mailing list [email protected] https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=jVj56eFZMBdw2XTy1WmujjlEfwGR4yGcPx8hs15Otm8&r=SqEE8dddEcFzYmSZdqK2NnlRtkrj2jI_1dLmK8Yaacg&m=iuTtMGmiC9yV3rl1fyKeu2DVYym7MtYKBqjGuiv5GZE&s=2tSlfGc5F-IP8q1UYRidxg_4QvrztY_q70OY5_HSSAM&e= _______________________________________________ Sprinklerforum mailing list [email protected] https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=jVj56eFZMBdw2XTy1WmujjlEfwGR4yGcPx8hs15Otm8&r=SqEE8dddEcFzYmSZdqK2NnlRtkrj2jI_1dLmK8Yaacg&m=iuTtMGmiC9yV3rl1fyKeu2DVYym7MtYKBqjGuiv5GZE&s=2tSlfGc5F-IP8q1UYRidxg_4QvrztY_q70OY5_HSSAM&e= _______________________________________________ Sprinklerforum mailing list [email protected] https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=jVj56eFZMBdw2XTy1WmujjlEfwGR4yGcPx8hs15Otm8&r=SqEE8dddEcFzYmSZdqK2NnlRtkrj2jI_1dLmK8Yaacg&m=iuTtMGmiC9yV3rl1fyKeu2DVYym7MtYKBqjGuiv5GZE&s=2tSlfGc5F-IP8q1UYRidxg_4QvrztY_q70OY5_HSSAM&e= _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org