Travis, NFPA 20 only requires that the room be sized "to fit" with clearance for access. While that clearance is required, there is no set amount of clearance defined.
From the 2019 edition: "4.14.1.1.7 The pump room or pump house shall be sized to fit all of the components necessary for the operation of the fire pump and to accommodate the following: (1) Clearance between components for installation and maintenance (2) Clearance between a component and the wall for installation and maintenance (3) Clearance between energized electrical equipment and other equipment in accordance with NFPA 70 (this one has requirements that you've already met.) (4) Orientation of the pump to the suction piping to allow compliance with 4.16.6.3 (this would be the '10 pipe diameter rule' for certain suction piping.) Sorry, I don't have any other substantiation for ya. It should be recognized that the above is my opinion as a member of the NFPA, and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee Projects and should therefore not be considered, nor relied upon, as the official position of the NFPA, nor any of their technical committees. Sincerely, Cecil Bilbo Academy of Fire Sprinkler Technology Champaign, IL 217.607.0325 www.sprinkleracademy.com<http://www.sprinkleracademy.com> [email protected]<mailto:[email protected]> OUR STUDENTS SAVE LIVES!! ________________________________ From: Sprinklerforum <[email protected]> on behalf of Travis Mack via Sprinklerforum <[email protected]> Sent: Thursday, November 5, 2020 3:38 PM To: [email protected] <[email protected]> Cc: [email protected] <[email protected]> Subject: Clearance around all pump equipment Is there anything in any fire code or standard that requires a 3' clearance around ALL pump room equipment. We are maintaining 3' clear of controllers. It is being brought up he wants 3' clear of everything. We asked for a reference. The response was "in the book." Any help or guidance? Travis Mack, CFPS, CWBSP, RME-G, SET Engineering Manager MFP Design 3356 E Vallejo Ct Gilbert, AZ 85298 NEW EXTENSION: 480-505-9271 ext. 700 NEW MOBILE: 480-272-2471 [email protected] www.mfpdesign.com<http://www.mfpdesign.com> Send large files to us via: https://www.hightail.com/u/MFPDesign LinkedIn: https://www.linkedin.com/in/travismack “The bitterness of poor quality remains long after the sweetness of low price is forgotten.” Need/Want a faster way to check material pricing? Build a material quote? Check availability ? Searching for an invoice? *If you do not already have an account with ferguson.com, click here to register.* **Have a Ferguson account? Download the Ferguson app for on-the-go access to your favorite ferguson.com features. Apple iOS devices or Android devices** _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org