Travis,

NFPA 20 only requires that the room be sized "to fit" with clearance for 
access.  While that clearance is required, there is no set amount of clearance 
defined.

From the 2019 edition:
"4.14.1.1.7 The pump room or pump house shall be sized to fit all of the 
components necessary for the operation of the fire
pump and to accommodate the following:
(1) Clearance between components for installation and maintenance
(2) Clearance between a component and the wall for installation
and maintenance
(3) Clearance between energized electrical equipment and
other equipment in accordance with NFPA 70 (this one has requirements that 
you've already met.)
(4) Orientation of the pump to the suction piping to allow
compliance with 4.16.6.3 (this would be the '10 pipe diameter rule' for certain 
suction piping.)

Sorry, I don't have any other substantiation for ya.

It should be recognized that the above is my opinion as a member of the NFPA, 
and has not been processed as a formal interpretation in accordance with the 
NFPA Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the NFPA, nor any of 
their technical committees.

Sincerely,


Cecil Bilbo
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
www.sprinkleracademy.com<http://www.sprinkleracademy.com>
[email protected]<mailto:[email protected]>

OUR STUDENTS SAVE LIVES!!


________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Travis Mack via Sprinklerforum <[email protected]>
Sent: Thursday, November 5, 2020 3:38 PM
To: [email protected] 
<[email protected]>
Cc: [email protected] <[email protected]>
Subject: Clearance around all pump equipment

Is there anything in any fire code or standard that requires a 3' clearance 
around ALL pump room equipment.  We are maintaining 3' clear of controllers.  
It is being brought up he wants 3' clear of everything.  We asked for a 
reference.  The response was "in the book."

Any help or guidance?


Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
[email protected]
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

Need/Want a faster way to check material pricing?  Build a material quote?  
Check availability ?   Searching for an invoice?
*If you do not already have an account with ferguson.com, click here to 
register.*
**Have a Ferguson account? Download the Ferguson app for on-the-go access to 
your favorite ferguson.com features. Apple iOS devices or Android devices**

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to