Just throwing this out there, how many designers add a note to the drawings indicating the signage required at the fire department connection indicating the pressure required to deliver the standpipe system demand as per NFPA #14 section 6.4.5.2.2 (2016ed).
On a second note we have a building that is sprinklered and has a standpipe and as such the standpipe demand when calculated is 63psi @ 500gpm at the top most outlets, so the pressure required to deliver this is 112psi at the inlet of the Siamese connection, this was what we put on the sign. I have been advised that this is wrong and the pressure would be 149psi at the inlet as this would then deliver 100psi at the hose valve. Comments? Thank You James Crawford Phaser Fire Protection Ltd. Phone 604-888-0318 Cel: 604-790-0938 Email [email protected]<mailto:[email protected]> Web: www.phaserfire.ca<http://www.phaserfire.ca> _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org