Our building code allows the pressure at the top most outlet to be less than 
100psi if the building is sprinkled and a fire pump is not used to make the 
system work, city pressure only, but the pipe size of the standpipe must be 
sized to allow the fire department to provide the required flow.

So based on the above our system demand was 112psi @ 500gpm

Thank You

James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Cel: 604-790-0938
Email [email protected]
Web: www.phaserfire.ca

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Steve Leyton via Sprinklerforum
Sent: Wednesday, November 25, 2020 9:16 AM
To: [email protected]
Cc: Steve Leyton <[email protected]>; [email protected]
Subject: RE: Standpipe signage

Yep.


Steve Leyton

(Sent from my smartphone; please excuse typos and voice-to-text corruptions.)



-------- Original message --------
From: Travis Mack via Sprinklerforum <[email protected]>
Date: 11/25/20 8:59 AM (GMT-08:00)
To: [email protected]
Cc: [email protected]
Subject: RE: Standpipe signage

Yes, we always include the note about the required flow/pressure required at 
the FDC inlet.  I believe that requirement is straight from NFPA 14.

As to your other question, if you have 100 psi needed at the top, how can you 
have a demand of 63 psi at the supply?  Assuming this is a manual wet 
standpipe, then your supply is the FDC.  And yes, you would need 100 psi + 
elevation pressure + friction losses.  So you may need the 149 psi.  It is 
dependent on your calcs.


Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
mailto:[email protected]
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0
LinkedIn: 
https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

Need/Want a faster way to check material pricing?  Build a material quote?  
Check availability ?   Searching for an invoice?
*If you do not already have an account with ferguson.com, click 
https://www.ferguson.com/account-registration to register.* **Have a Ferguson 
account? Download the Ferguson app for on-the-go access to your favorite 
ferguson.com features. 
http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003
 or 
http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003**

From: Sprinklerforum <[email protected]> On Behalf 
Of James Crawford via Sprinklerforum
Sent: Wednesday, November 25, 2020 9:49 AM
To: [email protected]
Cc: James Crawford <[email protected]>
Subject: Standpipe signage

Just throwing this out there, how many designers add a note to the drawings 
indicating the signage required at the fire department connection indicating 
the pressure required to deliver the standpipe system demand as per NFPA #14 
section 6.4.5.2.2 (2016ed).

On a second note we have a building that is sprinklered and has a standpipe and 
as such the standpipe demand when calculated is 63psi @ 500gpm at the top most 
outlets, so the pressure required to deliver this is 112psi at the inlet of the 
Siamese connection, this was what we put on the sign. I have been advised that 
this is wrong and the pressure would be 149psi at the inlet as this would then 
deliver 100psi at the hose valve.

Comments?

Thank You

James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Cel: 604-790-0938
Email mailto:[email protected]<mailto:[email protected]>
Web: http://www.phaserfire.ca<http://www.phaserfire.ca>

_______________________________________________
Sprinklerforum mailing list
mailto:[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to