On Fri, May 7, 2021 at 11:23 AM Michael Hill via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> There goes my logic, right out the window......again.
>
> Mike Hill
>
> -----Original Message-----
> From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On
> Behalf Of Bob Caputo via Sprinklerforum
> Sent: Friday, May 7, 2021 2:21 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Bob Caputo <bcap...@firesprinkler.org>
> Subject: Re: Available Pressure from Fire Water Storage Tank
>
> No, you are not permitted to use elevation pressure from a gravity tank.
> You do not know the elevation of the water in the tank which is depleted
> during the operation of the systems in fighting the fire.  You are
> permitted to use the pumps productive curve at 150% of rated flow and 65%
> of rated pressure
>
> On Fri, May 7, 2021 at 11:13 AM Kyle.Montgomery via Sprinklerforum <
> sprinklerforum@lists.firesprinkler.org> wrote:
>
> > I'm working on a project where they are adding a new building to an
> > existing campus. There is an existing fire water storage tank and fire
> > pump  that serves the site underground fire loop. The new building has
> > a very demanding sprinkler system that just barely exceeds the fire
> > pump's pressure available at the demand flow (using just the pump
> > curve as the water supply).
> >
> > Normally, I would be conservative and use just a few psi as my water
> > supply from the tank (as though it were nearly empty). But, is that
> > overly conservative? The tank is mounted on the ground, at the same
> > elevation as the fire pump, but it is nearly 45 feet tall, with a
> > total capacity of over
> > 500,000 gallons. Can I use some of that elevation pressure, or do I
> > need to design and calc as though the tank is nearly depleted?
> >
> > -Kyle M
> > _______________________________________________
> > Sprinklerforum mailing list
> > Sprinklerforum@lists.firesprinkler.org
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
> --
> Bob Caputo, CFPS
> *President*
>
> *American Fire Sprinkler Association*
> p: 214-349-5965 ext124
> w: firesprinkler.org
> <https://www.facebook.com/firesprinkler.org/>
> <https://twitter.com/afsa/status/1039528345367732224>
> <
> https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/
> >
>    <https://www.instagram.com/firesprinklerorg/>
>
> *Train a safer, more efficient workforce.*
>
> By enrolling your employees in the AFSA Apprenticeship Training Series for
> Sprinkler Fitters <
> https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149
> >,
> you will reap the benefits of a qualified, professional installation crew.
> Well-trained employees will work smarter, increasing your company's
> productivity and, in turn, its profits. Learn more <
> https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149
> >
> .
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
-- 
Bob Caputo, CFPS
*President*

*American Fire Sprinkler Association*
p: 214-349-5965 ext124
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Train a safer, more efficient workforce.*

By enrolling your employees in the AFSA Apprenticeship Training Series for
Sprinkler Fitters
<https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>,
you will reap the benefits of a qualified, professional installation crew.
Well-trained employees will work smarter, increasing your company's
productivity and, in turn, its profits. Learn more
<https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>
.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to