JP Shutoff 160
JP Cutin 150
FP1 Cutin 145
FP2 Cutin 140

FP1 and FP2 are Patterson HSC 1250 NET 120s with steel bolted 30 foot tanks.  
These are filled per UFC 03-600-01 with 200 GPM each well head pumps.  The fill 
rates are NOT per NFPA but UFC.  Controllers are Tornatech soft start.

Don't know actual flow rate but it should  be less than a standard 5.6K 
residential for the barracks.  Yet to confirm.  Good question.

Main is 12".  All laterals and risers are 6".


Design was per 2013 UFC with some modifications.  USACE.  My AHJ is 
USNAVFACENGCOM.

JP is supervised on, off and run.

Heat trace is also supervised, on and off.



________________________________
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> on behalf 
of Mike Morey via Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Sent: Thursday, November 18, 2021 10:50 PM
To: sprinklerforum@lists.firesprinkler.org 
<sprinklerforum@lists.firesprinkler.org>
Cc: Mike Morey <mmo...@shambaugh.com>
Subject: RE: Fire Pump Shutdown

Interesting scenario, if I can ask what are the starts and stops of the JP and 
FP?  And what flow rating is the Jockey?  That seems like a lot of flow for the 
jockey to build pressure back up high enough to cut the fire pump back out and 
leave it off after 10 minutes, and if the Jockey keeps up it's kind of 
surprising the initial drop is fast enough to bring both in before leveling off.

Mike Morey
CFPS 3229 . NICET S.E.T. 123677
Project Manager . Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive . Fort Wayne, IN . 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email mmo...@shambaugh.com



-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of BF Blake via Sprinklerforum
Sent: Thursday, November 18, 2021 2:44 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: BF Blake <bfbl...@hotmail.com>
Subject: Re: Fire Pump Shutdown


BE ADVISED - This email originated outside EMCOR.


Mike,

Thanks

In my case I can operate the ITC and get JP and FP to start, then FP stops at 
10 minutes with the 1/2" still open and flowing.

The ITC calculated flow is 70 GPM, the FP is 1250 GPM.  Central station 
reporting is NOT operational here, but that is a side note.

FP will not auto restart unless I open more heads, which in a real world fire 
scenario is exacrly what will happen

This is designed under 2013 UFC 03-600-01.

Thank You Sir.

Byron

________________________________
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> on behalf 
of Mike Morey via Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Sent: Thursday, November 18, 2021 10:38 PM
To: sprinklerforum@lists.firesprinkler.org 
<sprinklerforum@lists.firesprinkler.org>
Cc: Mike Morey <mmo...@shambaugh.com>
Subject: RE: Fire Pump Shutdown

I've always understood it to be allowed even for a non-testing situation if 
approved.  The 2019 edition clarified this somewhat by breaking out automated 
testing as essentially ok even without specific approval and then a separate 
line item for when approved by the AHJ.  In places where the pump may not 
readily get shut off during an accidental start the 10 minute timer makes a lot 
of sense.  Timer only starts when shutoff pressure is reached and start 
pressure isn't dropped below again for 10 minutes, and even then pump would 
immediately restart if pressure dropped again.  I've always felt we were pretty 
conservative in how rarely it's utilized.

Mike Morey
CFPS 3229 . NICET S.E.T. 123677
Project Manager . Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive . Fort Wayne, IN . 46825 direct 260.487.7824 /  cell 
260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com



-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of BF Blake via Sprinklerforum
Sent: Thursday, November 18, 2021 2:27 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: BF Blake <bfbl...@hotmail.com>
Subject: Fire Pump Shutdown


BE ADVISED - This email originated outside EMCOR.


Greetings Forum Members

Do we believe it is the intent of NFPA 20 TC is  for 10 minute automatic shut 
down (when enabled) of fire pumps to apply only during churn (e.g. dead head, 
closed loop, testing) conditions or to any condition to include sprinkler flow 
(e.g. 1/2" 5.6K ITC flow)?

Is the intent to protect the fire pump from "burn out"?  Is the intent to run 
pumps to failure (destruction) or is the intent, with 10 minute auto shut down, 
where permitted, to attempt to preserve the pump?

Thanks

Byron
NATO Facility
UFC Criteria 03-600-01 (2013) Applicable SÅ‚upsk, Pomorskie, Poland

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.com%2Fv3%2F__https%3A%2F%2Femea01.safelinks.protection.outlook.com%2F%3Furl%3Dhttps*3A*2F*2Furldefense.com*2Fv3*2F__http*3A*2F*2Flists.firesprinkler.org*2Flistinfo.cgi*2Fsprinklerforum-firesprinkler.org__*3B!!FaxH778!OB4oaFijo2IZH9_K4Ka5cxdQY-nT0eZ81GZKqVwxU8Aeda74ceQbgz-mcJ3IOTAl*24%26amp%3Bdata%3D04*7C01*7C*7Cf2648ec125f9440f235908d9aacb0a30*7C84df9e7fe9f640afb435aaaaaaaaaaaa*7C1*7C0*7C637728611294808875*7CUnknown*7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0*3D*7C3000%26amp%3Bsdata%3DEZZRoWI6b6t76V0UlLXC2OcaVH*2FH34GSwuTYaMzniMA*3D%26amp%3Breserved%3D0__%3BJSUlJSUlJSUlJSUlJSUlJSUlJSUlJSUlJQ!!FaxH778!JzPkyBsLK-ey3XCE32nnATIgFkW5AeWvKDHJ42XdMM6iQopQJmPgvxsSdbqvG4z2%24&amp;data=04%7C01%7C%7C38857b5f6d2147c2cc0408d9aacca175%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728618123547118%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=3TSaYUlfiD5SRK91Y1VmpyL3jVZLIeZZDE4AJaruUM0%3D&amp;reserved=0

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.com%2Fv3%2F__https%3A%2F%2Femea01.safelinks.protection.outlook.com%2F%3Furl%3Dhttp*3A*2F*2Flists.firesprinkler.org*2Flistinfo.cgi*2Fsprinklerforum-firesprinkler.org%26amp%3Bdata%3D04*7C01*7C*7Cf2648ec125f9440f235908d9aacb0a30*7C84df9e7fe9f640afb435aaaaaaaaaaaa*7C1*7C0*7C637728611294808875*7CUnknown*7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0*3D*7C3000%26amp%3Bsdata%3DhWNBg1tc1HmbEF82*2BR6vESHmcaLBE3UaF1ECiqPBV7g*3D%26amp%3Breserved%3D0__%3BJSUlJSUlJSUlJSUlJSUlJSUl!!FaxH778!JzPkyBsLK-ey3XCE32nnATIgFkW5AeWvKDHJ42XdMM6iQopQJmPgvxsSddyvZEgl%24&amp;data=04%7C01%7C%7C38857b5f6d2147c2cc0408d9aacca175%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728618123557109%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=8UlIC9M2Vs8gfoNuiCsj3Fi9EOpPetIygtI3G6VrM%2Bk%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.com%2Fv3%2F__http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org__%3B!!FaxH778!JzPkyBsLK-ey3XCE32nnATIgFkW5AeWvKDHJ42XdMM6iQopQJmPgvxsSdXjTyE7m%24&amp;data=04%7C01%7C%7C38857b5f6d2147c2cc0408d9aacca175%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728618123557109%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=2IfPC%2Btr05l%2B3y%2BgMa1xMfwtDu0lM20Czo0fl586Tw4%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7C%7C38857b5f6d2147c2cc0408d9aacca175%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637728618123557109%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=iVqFrFeFyfyXuM%2F08m4UhDdOUkPvKU96KfzVKiGrIxw%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to