Arguably in the right circumstances the tub or shower enclosure could be come a 
separate "compartment" I would think.  We don't do a ton of this but a lot of 
higher end properties have a toilet cubicle that usually qualifies as a 
compartment and doesn't require a separate sprinkler in just it.  Typically the 
rest of the bathroom is well over 55 sq ft in these types of residences though.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email mmo...@shambaugh.com



-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Tuesday, January 11, 2022 2:14 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: travis.m...@mfpdesign.com; wmens...@comcast.net
Subject: RE: 13R bathrooms

 
BE ADVISED - This email originated outside EMCOR. 
 

Tub area is to be included.  I believe there was confusion as it wasn't always 
being applied correctly, so the committee just said 55 sq ft total.

Travis Mack, CFPS, CWBSP, RME-G, COC, SET Senior Engineering Manager MFP Design
480-505-9271 ext. 700 C: 480-272-2471
travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>
https://urldefense.com/v3/__http://www.mfpdesign.com__;!!FaxH778!P_yUSvDLtBo4axv33XGiyC5qBELehWPhsE3N-ckNJmcig1itRc9bHGgOG2lEb9_s$
 
<https://urldefense.com/v3/__http://www.mfpdesign.com__;!!FaxH778!P_yUSvDLtBo4axv33XGiyC5qBELehWPhsE3N-ckNJmcig1itRc9bHGgOG2lEb9_s$
 >

Send large files to us via: 
https://urldefense.com/v3/__https://www.hightail.com/u/MFPDesign__;!!FaxH778!P_yUSvDLtBo4axv33XGiyC5qBELehWPhsE3N-ckNJmcig1itRc9bHGgOG56tm3Aw$
 
<https://urldefense.com/v3/__https://na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.hightail.com*2Fu*2FMFPDesign&data=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5*2BAZvlHhABSexWY*3D&reserved=0__;JSUlJSUlJSUlJSUlJSU!!FaxH778!P_yUSvDLtBo4axv33XGiyC5qBELehWPhsE3N-ckNJmcig1itRc9bHGgOG4pGJO3Q$
 >

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of BILL MENSTER via Sprinklerforum
Sent: Tuesday, January 11, 2022 11:53 AM
To: sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Cc: BILL MENSTER <wmens...@comcast.net>
Subject: 13R bathrooms

I believe past editions of NFPA 13R (pre-2007) included an explanation that the 
bathtub area need not be included in the square foot area of the bathroom. 
However, current editions (in this case the 2016 edition) do not include this 
language. My question is, does the tub area need to be included in the bathroom 
area?
Thanks for your help.


Bill Menster

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!P_yUSvDLtBo4axv33XGiyC5qBELehWPhsE3N-ckNJmcig1itRc9bHGgOG3rr_Snv$
 
<https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!P_yUSvDLtBo4axv33XGiyC5qBELehWPhsE3N-ckNJmcig1itRc9bHGgOG3rr_Snv$
 > _______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!P_yUSvDLtBo4axv33XGiyC5qBELehWPhsE3N-ckNJmcig1itRc9bHGgOG3rr_Snv$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to