Take it a step farther.  You need to look at all the various areas within the 
building.  For multi-use buildings, you can have various levels of hazards 
under one roof.  This is one reason why you can't use the annex as an end-all 
of occupancies.



Tall, open areas need to be looked at differently than standard height 8-10 ft 
areas.



Look at your sprinkler listings. A sprinkler Listed for LH may have a ceiling 
height limitation.



Don't ya just love the wild and wooly world of fire protection?  😊



Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
craig.pr...@jacobs.com | www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

CONTACT BY: email or MS TEAMS







-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Bob Caputo via Sprinklerforum
Sent: Monday, February 7, 2022 8:58 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Bob Caputo <bcap...@firesprinkler.org>; tston...@comcast.net
Subject: [EXTERNAL] RE: INDOOR SPORTS FACILITY FIELD HOUSE



Not in my opinion.  We should always look at the definitions for each occupancy 
classification as opposed to the list in the annex.  These facilities have a 
lot of plastics and combustibles that exceed the definition of light hazard and 
they are of heights exceeding 8 ft so OH1 is probably not adequate.



When I look at the foam in landing pits of gymnasiums or even the bleachers, 
I'd have a hard time seeing a simple gymnasium as light hazard.



This is a personal opinion.



Bob Caputo, CFPS

President

American Fire Sprinkler Association





-----Original Message-----

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of tstone52--- via Sprinklerforum

Sent: Monday, February 7, 2022 7:44 AM

To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>

Cc: tston...@comcast.net<mailto:tston...@comcast.net>

Subject: INDOOR SPORTS FACILITY FIELD HOUSE



NFPA does not define Field houses.



Indoor Track, Basketball Courts, Tennis Courts and Climbing Wall. The new 
building will be 37'-0 high to the peak of a flat roof.







Would it be safe to use Light Hazard Occupancy?











Regards,



G. Tim Stone







G. Tim Stone Consulting, LLC



NICET Level III Engineering Technician



Fire Protection Sprinkler Design



and Consulting Services







   117 Old Stage Rd. - Essex Jct., VT. 05452



                 CELL: (802) 373-0638



              <mailto:tston...@comcast.net> 
tston...@comcast.net<mailto:tston...@comcast.net>







_______________________________________________

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>

https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o__;!!B5cixuoO7ltTeg!ST2dG3hqxRkvBw-dzx61kx0gBeM41Dd__thMJ_eFqHAjzCxZygMolAa1ML5_7cG_uA$<https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o__;!!B5cixuoO7ltTeg!ST2dG3hqxRkvBw-dzx61kx0gBeM41Dd__thMJ_eFqHAjzCxZygMolAa1ML5_7cG_uA$>

rg

_______________________________________________

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>

https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!ST2dG3hqxRkvBw-dzx61kx0gBeM41Dd__thMJ_eFqHAjzCxZygMolAa1ML4wgnIYqQ$<https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!ST2dG3hqxRkvBw-dzx61kx0gBeM41Dd__thMJ_eFqHAjzCxZygMolAa1ML4wgnIYqQ$>

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to