Craig, the joists are 12” deep, 16” o.c.  The entire depth and width of the 
joist is filled with noncombustible insulation. 

Sent from my iPhone

> On Feb 16, 2022, at 6:55 AM, Prahl, Craig/GVL via Sprinklerforum 
> <sprinklerforum@lists.firesprinkler.org> wrote:
> 
> What are the depths of the joists, the depth of the insulation and the 
> spacing between the joists?
> 
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
> craig.pr...@jacobs.com | www.jacobs.com
> 1041 East Butler Road   Greenville, South Carolina  29606
> CONTACT BY: email or MS TEAMS
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On 
> Behalf Of Scott Harvey via Sprinklerforum
> Sent: Wednesday, February 16, 2022 12:53 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Scott Harvey <sc...@harveyplumbing.com>
> Subject: [EXTERNAL] Obstructed vs Unobstructed Construction
> 
> Hi all, I have a question for the group.
> 
> I've got a storeroom, ceiling is open to structure.  The roof structure is 
> solid wood joists, which are fully insulated between each joist.
> 
> We have installed standard spray upright sprinklers with the deflectors 
> approx 8-10 inches below the bottom of the joist/insulation.
> 
> In my mind, this is unobstructed construction, because per "A.8.5.4.1 Batt 
> insulation creates an effective thermal barrier and can be considered the 
> ceiling/roof deck when determining distances between deflector and ceiling."  
> Chapter 3 defines Obstructed Construction "Panel construction and other 
> construction where beams, trusses, or other members impede heat flow or water 
> distribution in a manner that materially affects the ability of the sprinkler 
> to control or suppress a fire".
> 
> Now that I look at this again, I'm thinking I am wrong and should be 
> obstructed construction because although the batt insulation creates a 
> thermal barrier (similar to a smooth ceiling) the structure is still the 
> same, so I would need to keep my upright sprinklers max 6-inches below the 
> bottom of structure?
> 
> Would appreciate input from the group.
> 
> 
> Thanks,
> 
> Scott Harvey, CET
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!WNJbuEDrG9DqZDyEL512vMojwZ-VOZeVutCjsR6asnXWsu5WOOUl9NA1aE0ZoG95hg$
> 
> ________________________________
> 
> NOTICE - This communication may contain confidential and privileged 
> information that is

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to