What T-Mack said. It is "alluded" to use higher K's in 19.3.3.2.7 of the 2019 edition..
R/ Matt -----Original Message----- From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of Travis Mack via Sprinklerforum Sent: Tuesday, March 8, 2022 7:50 AM To: sprinklerforum@lists.firesprinkler.org Cc: Travis Mack <travis.m...@mfpdesign.com> Subject: RE: .25 or better The key thing in NFPA 13 is LOCATION MATTERS. The statement about needing ≥K8 at ≥0.20 density and ≥K11.2 at ≥0.34 density is in Chapter 12 of the 2016 edition. Chapter 12 is for storage. So, you could extra hazard grp II and use K8 sprinklers because it is not storage. As Roland Huggins would always remind me. LOCATION MATTERS. So, if your project is storage, that comes in to plan in the General Requirements for Storage section. If it is not storage, then those sections don’t apply. Please rate our customer service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication> Travis Mack, CFPS, CWBSP, RME-G, COC, SET Senior Engineering Manager MFP Design 480-505-9271 ext. 700 C: 480-272-2471 travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com> www.mfpdesign.com<http://www.mfpdesign.com> Send large files to us via: https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0> From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of Vince Sabolik via Sprinklerforum Sent: Tuesday, March 8, 2022 7:47 AM To: sprinklerforum@lists.firesprinkler.org Cc: Vince Sabolik <vi...@wtfp.net> Subject: .25 or better Good morning, forum Can someone give me chapter & verse of the NFPA 13 statement that you can't use 1/2" heads when the density is .25 or better? thanks, Vince -- 11351 Pearl Road / Suite 101 Strongsville, Ohio 44136 Phone 440 238-4800 Fax 440 238-4876Cell 440 724-7601 / Vince Sabolik / _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org