Thanks, Travis. I thought that I had the wrong reference.
Once upon a time it SAID don't use 1/2" heads when the density is .25 or
more.
Or, am I crazy?
Forum moderator: Please limit number of answers!
thanks, Vince
On 3/8/2022 9:50 AM, Travis Mack via Sprinklerforum wrote:
The key thing in NFPA 13 is LOCATION MATTERS. The statement about needing ≥K8
at ≥0.20 density and ≥K11.2 at ≥0.34 density is in Chapter 12 of the 2016
edition. Chapter 12 is for storage. So, you could extra hazard grp II and use
K8 sprinklers because it is not storage.
As Roland Huggins would always remind me. LOCATION MATTERS.
So, if your project is storage, that comes in to plan in the General
Requirements for Storage section. If it is not storage, then those sections
don’t apply.
Please rate our customer
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>
Travis Mack, CFPS, CWBSP, RME-G, COC, SET
Senior Engineering Manager
MFP Design
480-505-9271 ext. 700 C: 480-272-2471
travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>
www.mfpdesign.com<http://www.mfpdesign.com>
Send large files to us
via:https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
From: Sprinklerforum<sprinklerforum-boun...@lists.firesprinkler.org> On Behalf
Of Vince Sabolik via Sprinklerforum
Sent: Tuesday, March 8, 2022 7:47 AM
To:sprinklerforum@lists.firesprinkler.org
Cc: Vince Sabolik<vi...@wtfp.net>
Subject: .25 or better
Good morning, forum
Can someone give me chapter & verse of the NFPA 13
statement that you can't use 1/2" heads when the density
is .25 or better?
thanks, Vince
--
11351 Pearl Road / Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876Cell 440 724-7601
/
Vince Sabolik /
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
11351 Pearl Road / Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876Cell 440 724-7601
/
Vince Sabolik /
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org