I don't think any of these codes would apply to this situation as a water
curtain as described above is within a sprinklered area, I think in this
situation you would not be installing a water curtain, this would be more
of a fire separation, IMO this is a bit outside of NFPA 13 and someone
needs to determine an amount of water required to create the fire
separation. The water curtain requires 3gpm per lineal foot but as a fire
separation this may need to be increased.

Thanks

Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca




On Mon, Mar 21, 2022 at 3:09 PM Sergio Braga <sergioweling...@gmail.com>
wrote:

> We have a small restaurant project where we are designing a water curtain
> for fire separation of open kitchen and dining area. The building is not
> required to be fully sprinklered.
>
> Regarding the hydraulic calculations for the water curtain, I will mention
> the applicable code sections:
>
> NFPA13-2007: 11.2.3 Water Demand Requirements - Hydraulic Calculation
> Methods.
> 11.2.3.1.1 The water supply for sprinklers shall be determined only from
> one of the following:
> (1) Density/area curves of Figure 11.2.3.1.1 in accordance with the method
> of 11.2.3.2
> (2) On the basis of the room design method in accordance with 11.2.3.3
> (3) Special design areas in accordance with 11.2.3.4, at the discretion of
> the designer
>
> NFPA13-2007: 11.3 Special Design Approaches.
> NFPA13-2007: 11.3.3 Water Curtains.
> 11.3.3.1 Sprinklers in a water curtain such as described in 8.15.4 or
> 8.15.16.2 shall be hydraulically designed to provide a discharge of 3 gpm
> per lineal foot (37 L/min per lineal meter) of water curtain, with no
> sprinklers discharging less than 15 gpm (56.8 L/min) .
> 11.3.3.2 For water curtains employing automatic sprinklers, the number of
> sprinklers calculated in this water curtain shall be the number in the
> length corresponding to the length parallel to the branch lines in the area
> determined by 22.4.4.1.1.
> 11.3.3.3 If a single fire can be expected to operate sprinklers within the
> water curtain and within the design area of a hydraulically calculated
> system, the water supply to the water curtain shall be added to the water
> demand of the hydraulic calculations and shall be balanced to the
> calculated area demand.
> 11.3.3.4 Hydraulic design calculations shall include a design area
> selected to include ceiling sprinklers adjacent to the water curtain.
>
> If I perform the hydraulic calculation per density/area method the
> existing water supply system will not be capable of meeting the demand.
> However, I believe I am going to the wrong direction since this is only a
> water curtain system, and I think the density and area of sprinkler
> operation from FIGURE 11.2.3.1.1 is not applicable.
>
> What do you guys think?
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to