As far as I know - code says "if the building is type V". I am not an IBC/IFC 
expert, but I don't think that you can change a type 5 building into anything 
else based on just the balconies.

One gotcha (that got me once) - if the building is Type 3, 4, or 5 and the 
patio/balcony is type 5 and not fire rated or FRT wood, then you will probably 
need sprinklers out there too! That is 13 and 13R even if it is not covered (by 
the letter of the code). [IBC 2018 edition, section 705.2.3.1]

I would plan on sprinklers.

Matt


From: travis.m...@mfpdesign.com <travis.m...@mfpdesign.com>
Sent: Wednesday, May 18, 2022 10:43 PM
To: slock...@aitlifesafety.com; sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Re: Non-combustible patio/balcony in 13R Type V 
construction

If type 5 I still put one out there.


Travis Mack, CFPS, CWBSP, RME-G, COC, SET

Senior Engineering Manager

MFP Design

480-505-9271 ext. 700<tel:480-505-9271;700> C: 480-272-2471<tel:480-272-2471>

travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>

www.mfpdesign.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.mfpdesign.com%2f&c=E,1,N0QJ7cbHjBs-IJEE5nLaOcJfLVNKwLjPODSa-Jwcwfv888rW6U2Bz9cfERPpvirHMY6MJDv0DEHQ2xhpC11Dvsa44sLS7y9Mv7520lHlmw,,&typo=1>



Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>

________________________________
From: Sean Lockyer 
<slock...@aitlifesafety.com<mailto:slock...@aitlifesafety.com>>
Sent: Wednesday, May 18, 2022 5:45:02 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Non-combustible patio/balcony in 13R Type V 
construction

Per the Florida Building Code, Chapter 9, sprinkler protection is required for 
an exterior balcony in a 13R system if the building is of Type V construction. 
However, that also assumes that the balcony overhang is also type V (I.E. - 
wood) but what would you do if the balcony is NOT combustible and is comprised 
of light-gauge metal ? Is this a bit of a grey area or a jurisdictional call ?

            Sean Lockyer
            Project Designer                           6817 N. Orange Blossom 
Trail
            Cell    386-337-1078                            Orlando, Florida 
32810
            slock...@aitlifesafety.com<mailto:slock...@aitlifesafety.com>       
     Phone:    407-816-9101
            
www.AITLifeSafety.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.AITLifeSafety.com&c=E,1,hwyuN14Rz1Ub90kBOH8hYzRASQBa4CfpQvkIJvtogC9K0mrsEXrdgOQ514VQsVrgiie6e7kEm_Zd79l6XCfmjc_wBGf32V8E8k5KFtdNO8w,&typo=1>

















_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,q2Def0ZlvWOnj8vb21yvOvF5GxgB96Uom9Z0cKqKW4AdT7CZGhpArzaqBFl6Tam3e8E5PcYXw0dcg37VZZtwR5pWUUDHU6HCjbF7t_yihFvTrMD8sw,,&typo=1>
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to