Hello Sean-

This is also a requirement of NFPA 13R.
6.6.5.1 Where a roof or deck is provided above, sprinklers shall be
installed to protect attached exterior balconies, attached
exterior decks, and ground floor patios serving dwelling units in buildings
of Construction Type V.

My opinion to be able to exclude protection regardless of the materials is
if the attached exterior balconies, exterior decks, and ground floor patios
do NOT serve dwelling units of type V construction.

Thank you,


*Matthew Bristoll*
*Big Country Fire Protection, Inc.*
*106 Jumper Drive N.*
*Bushnell, FL 33513*
*C:239-398-1364*
*O:352-404-5990*


On Wed, May 18, 2022 at 8:43 PM Sean Lockyer <slock...@aitlifesafety.com>
wrote:

> Per the Florida Building Code, Chapter 9, sprinkler protection is required
> for an exterior balcony in a 13R system if the building is of Type V
> construction. However, that also assumes that the balcony overhang is also
> type V (I.E. - wood) but what would you do if the balcony is NOT
> combustible and is comprised of light-gauge metal ? Is this a bit of a grey
> area or jurisdictional call ?
>
>
>             Sean Lockyer
>             Project Designer                            6817 N. Orange
> Blossom Trail
>             Cell    386-337-1078                             Orlando,
> Florida 32810
>             slock...@aitlifesafety.com             Phone:    407-816-9101
>             www.AITLifeSafety.com
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to