The figure Mike is referring to is A.3.3.13 in the NFPA 24 (2022) edition.

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Senior Fire Protection Engineer
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
[email protected]  \  burnsmcd.com
8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout



-----Original Message-----
From: Hinson, Ryan <[email protected]> 
Sent: Wednesday, August 31, 2022 4:18 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: FDC Serving Multiple Buildings

NFPA 24 (2022) Section 5.9.1.2 states the following:
N 5.9.1.2 A single fire department connection shall be permitted to supply 
multiple buildings where acceptable to the AHJ.

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire Protection 
Engineer O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923 
[email protected]  \  burnsmcd.com
8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437 
*Registered in: AK, LA, MD, MN, PA, TX, & UT **NICET IV - Water-Based Systems 
Layout



-----Original Message-----
From: Kyle.Montgomery <[email protected]>
Sent: Wednesday, August 31, 2022 3:42 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: FDC Serving Multiple Buildings

That helps. Thanks a lot, Mike.

-Kyle M

-----Original Message-----
From: Mike Morey <[email protected]>
Sent: Wednesday, August 31, 2022 1:34 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Re: FDC Serving Multiple Buildings

NFPA 24 2019: 5.9.5.7
Where a remote fire department connection services multiple buildings, 
structures, or locations, a sign shall be provided indicating the buildings, 
structures, or locations served.

I don't know that it's in there anymore, didn't find it with a quick look, but 
there used to be a diagrammatic drawing of a "campus" fire loop with remote FDC 
as well somewhere in 13 or 24 I believe.

Mike Morey
CFPS 3229 . NICET S.E.T. 123677
Project Manager . Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive . Fort Wayne, IN . 46825 direct 260.487.7824 /  cell 
260.417.0625 /  fax 260.487.7991 email [email protected]



From: Kyle.Montgomery <[email protected]>
Sent: Wednesday, August 31, 2022 4:22 PM
To: [email protected]
Subject: [Sprinklerforum] FDC Serving Multiple Buildings

Is there any code requirement prohibiting a single FDC from serving multiple 
buildings on a site or campus? Or, better yet, is there a code reference that 
specifically allows this arrangement? We've done it quite a few times, but now 
ZjQcmQRYFpfptBannerStart Be Careful With This Message The sender's identity 
could not be verified and someone may be impersonating the sender. 


ZjQcmQRYFpfptBannerEnd
Is there any code requirement prohibiting a single FDC from serving multiple 
buildings on a site or campus? Or, better yet, is there a code reference that 
specifically allows this arrangement?

We've done it quite a few times, but now I've got a plan reviewer on a specific 
project stating that each of the buildings requires it's own FDC. He said we 
can file an appeal to use a single FDC, but I'm not sure what code section we 
would be appealing.

-Kyle M

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.

_________________________________________________________
SprinklerForum mailing list:
https://urldefense.com/v3/__https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!Ba8_KKAT!ITr4memymXUVhn3VyyfMxD-Q-iITT3q2UACh2lddFaOS032E2j26tfIGOOBodurr9fUh4vxAv2K8mov7v4Tq$
To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://nam12.safelinks.protection.outlook.com/?url=https%3A%2F%2Flists.firesprinkler.org%2Flist%2Fsprinklerforum.lists.firesprinkler.org&amp;data=05%7C01%7Crhinson%40burnsmcd.com%7Caa1f8337402843641d3f08da8b966be8%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C0%7C637975775461756100%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&amp;sdata=rWcH7ptYPgs7xg6s5qsifdOKzLaVgRVe3edwwQ8BqnA%3D&amp;reserved=0
To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://nam12.safelinks.protection.outlook.com/?url=https%3A%2F%2Flists.firesprinkler.org%2Flist%2Fsprinklerforum.lists.firesprinkler.org&amp;data=05%7C01%7Crhinson%40burnsmcd.com%7Caa1f8337402843641d3f08da8b966be8%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C0%7C637975775461756100%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&amp;sdata=rWcH7ptYPgs7xg6s5qsifdOKzLaVgRVe3edwwQ8BqnA%3D&amp;reserved=0
To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to