If it's serving a sprinkler system only and the main drain cannot flow a 
high-enough volume to match system demand, then you have to configure a means 
of testing that will, whether it's on the building or underground.   If the 
building is equipped with a fire pump and/or standpipes, you can check multiple 
boxes at a time by flow testing those components and the backflow 
simultaneously.

On the one hand, this ongoing conversation is getting close to kicking a dead 
horse, as I sense that many are making this a bigger deal than it has to be.   
On the other hand, if discussion like this can help form a set of standard/best 
practices, then this requirement can be readily incorporated into new builds 
and hopefully retrofitted as needed to existing systems.

Our industry is plagued by failed maintenance issues and we all should be as 
aware of and proactive as we can be on issues that facilitate implementation 
and enforcement of NFPA 25 nationwide.

Steve L.



From: Eric Rieve <e...@rievefire.com>
Sent: Wednesday, December 14, 2022 10:40 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: BFP on underground supply

You'll probably get some pretty diverse answers depending on how one views the 
intent behind the provision. The commentary advises using the full diameter of 
the riser as the outlet size to theoretically allow the test to be performed 
without needing to measure the flow with a pitot or hose monster setup. While 
this is true, and does adequately provide for exercising the backflow checks, 
it seems very wasteful to install a setup capable of flowing system demand and 
then not provide a few more inexpensive components that would allow the setup 
to accurately measure the flow (and pressure) from a hydraulic design 
perspective. While NFPA 25 doesn't require this accurate measurement 
specifically for the backflow exercise, it does require verifying the system 
demand from the private water main feeding that backflow at 5 year intervals.

Further, a fully functional flow test assembly has immeasurable uses when it 
comes to system modifications, and future water supply degradation testing that 
may someday be necessary. Finally, when filling out your aboveground 
certificate for system acceptance. I'd much rather know that I flowed system 
demand and maintained the appropriate residual pressure for the design as 
opposed to probably way overflowing demand through a full port opening and 
having an unusable pressure gauge reading.

Every riser is different obviously, and we've arranged them all sorts of ways 
depending on the situation. Sometimes we've used the single main drain and just 
installed a brass NPT x NST adapter on the exterior fitting. Other times we've 
installed one or two 2.5" NPT angle valves on saddles directly after the 
backflow with nipples through the wall to NST adapters on the exterior. 
Sometimes if the riser room has an exterior door we've just thrown two 2.5" 
angle hose valves on saddles or a grooved Siamese inlet. Our larger warehouse 
systems generally get a butterfly valve inside and full derby manifold on the 
exterior when they start getting into the 800gpm+ range. If you install an 
arrangement that allows for accurate waterflow measurement then you can prove 
your assembly meets the requirements.

Hope this helps!

Eric
Rieve Fire Protection


From: Dennis Wilson 
<dwil...@blackhawksprinklers.com<mailto:dwil...@blackhawksprinklers.com>>
Sent: Wednesday, December 14, 2022 12:01 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: BFP on underground supply

On backflow testing, NFPA 13 (2019) 16.14.5.1 states the backflow needs to be 
tested at system demand.
I have a hard cover copy, and in it the question was asked, if a 2" main drain 
would be sufficient, to do the backflow test.
After their explanation, they say it basically needs to be the same size as 
your system riser, and using a larger drain valve would be a waste since the 
drain test is to be done more often.
So what we've been doing is running a pipe outside the same size as the 
backflow, using a normally closed butterfly valve. Sometime routing around the 
FDC if it's a Storz. model.

Our thought now is why not run several 2" drains out the wall.
With 2½" & 3" backflows, we increase the main drain to 2" which is usually 
enough for system demand. Can always run a separate 1" insp. test also.
With 4" backflows, you already need (1) 2" main drain, why not run a separate 
one for testing, that will give you (2) 2" openings, and run a third if you 
have a 6" backflow.
And with multiple systems, run the main drains out separately instead of 
combining them together before you go out.

Does this sound feasible, since all we're really trying to do is exercise the 
springs in the checks?


From: Ed Kramer <e...@bamfordfire.com<mailto:e...@bamfordfire.com>>
Sent: Friday, November 18, 2022 11:19 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] BFP on underground supply

NFPA 13 is pretty clear that some method of forward flow testing a fire 
sprinkler system backflow preventer shall be provided.  If the BFP is located 
at the system riser (very common in these parts), we provide the required means.

So, who is responsible for providing the means if the BFP is located in a pit 
on the underground fire service, and the UG fire service (along with the 
pit/BFP) is "by others"?  From a practical viewpoint, it's easy enough for us 
to provide that at our system riser, but are we required to do so?  Or does 
that responsibility fall on whomever installs the BFP?  I've not seen this 
addressed anywhere in bid/contract documents.

Ed Kramer
Bamford Fire