I would agree, if they state .3 density rather than EH1 then they specifically 
wanted .3/2500 not Extra hazard 1 and applicable modifications.

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]
[cid:[email protected]]

From: Chris Dorn <[email protected]>
Sent: Tuesday, January 31, 2023 12:25 PM
To: [email protected]; Chris Dorn 
<[email protected]>
Subject: [Sprinklerforum] Clarification on 15.2.2.7(2) 2016 Ed.

The commodity that I am dealing with is solid piled group A plastics. Exposed, 
Expanded, Unstable, storage height >5 ft to <12 ft with max ceiling height of 
20’. The particular section of code which I am questioning is below. 15. 2. 2. 
7(2)
ZjQcmQRYFpfptBannerStart
This Message Is From an Untrusted Sender
You have not previously corresponded with this sender.
ZjQcmQRYFpfptBannerEnd
The commodity that I am dealing with is solid piled group A plastics. Exposed, 
Expanded, Unstable, storage height  >5 ft to <12 ft with max ceiling height of 
20’.

The particular section of code which I am questioning is below. 15.2.2.7(2) 
states that where table 15.2.2.5(a) allows densities and areas to be selected 
in accordance with Curve EH1 there are allowances for reduction of the 
hydraulic area to be reduced to 2000 square feet if 8.0 high temperature heads 
are used by applying 15.2.2.7(2)(a). When I look at the section of table 
15.2.2.5<https://urldefense.com/v3/__http:/15.2.2.5__;!!FaxH778!ZUIEI4eX9Gy1mvp4uU0Xa1Yfl3RgaWn9tgmtwIIrkvel0Y0HPLTqW10BLn01gbHvZGcuPM9oCs8r4mSulh1y-ddiNoJztQ$>
 the density called out is .3gpm. This is the density for EH1 but is not called 
out as EH1 on table 15.2.2.5(a).  My feeling is that while the density called 
out is .3gpm it is not specifically called EH1 like some of the other densities 
in the same table. Therefore I should calculate 2500 square feet per 
15.2.2.7(a) and I cannot apply 15.2.2.7(2)(a). Agree or disagree and why?



15.2.2.7* For Table 15.2.2.5(a) and Table 15.2.2.5(b), the design
areas shall be as follows:
(1) The area shall be a minimum of 2500 ft2 (232 m2).
(2) Where Table 15.2.2.5(a) and Table 15.2.2.5(b) allow densities
and areas to be selected in accordance with Curve
EH1 and Curve EH2 of Figure 13.2.1, any density/area
from the curves in Figure 13.2.1 shall be permitted. When
selecting a point from the EH1 or EH2 density/area
curves of Figure 13.2.1, the following area reductions
shall be permitted:
(a) For K-8.0 (115) sprinklers used with Curve EH1, the
design area shall be permitted to be reduced by
25 percent, but not below 2000 ft2 (186 m2), where
high temperature sprinklers are used.


[cid:[email protected]]



This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to