Let me chime in here as I'm somewhat confused on the conclusion.

 * Exposed group A plastics, expanded
 * Storage height > 5', and less than 12'
 * Max ceiling height 20'
 * Storage is solid piled
 * Storage is unstable

§15.2.2.1 directs me to the decision tree in Figure 15.2.2.1 and taking the above into account I end up with being directed to Table 15.2.6(a) or (b), and column C of that table.  I believe the table number is an errata in the standard as that specific table number - 15.2._*6*_(a) - does not exist in the '16 edition, and is likely meant to direct me to Table 15.2.2.5(a)

Following that decision tree to column "C" of the table, at a max storage height of 12', and a ceiling height not exceeding 20' that column shows a density of 0.5 gpm/ft².

§15.2.2.7.1 tells me the minimum remote area shall be 2500 ft².

The area modifications permitted do not apply as the density provided in the table is not per EH1 or EH2, and there's no information on what Chris shared that this is a closed array.

So I come up with a density of 0.5 gpm/ft² over a remote area minimum of 2,500 ft².

And in a quick look at the '22 edition, I come up with the same area/density, although the section and table numbers have changed (of course).

interesting question/problem,

*Ken Wagoner, SET*
*Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235*
*Phone: (760) 745-6181 *
*Visit the website <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>*
On 1/31/2023 1:03 PM, John Denhardt wrote:
Chris - you are correct.  This is a storage chapter and not an occupancy approach.  .3/2,500 period.  You are not using EH and reductions do not apply.

/The above is my opinion and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee Projects. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the //AFSA, and/or NFPA or its technical committees.//AFSA cannot provide design or consulting engineering services, and this opinion should therefore not be considered, nor relied upon, as such./
/
/
Thanks,
John

        
John August Denhardt, PE
/Vice President, Engineering and Technical Services/
*American Fire Sprinkler Association*
m: p:   301-343-1457
214-349-5965 ext 121
w:      firesprinkler.org <http://firesprinkler.org/>
<https://www.facebook.com/firesprinkler.org/> <https://twitter.com/afsa/status/1039528345367732224> <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/> <https://www.instagram.com/firesprinklerorg/>


*Our members are at the heart of everything we do.*


*/AFSA is on the move! /***

*Our new address is 1410 East Renner Rd., Suite 150, Richardson, TX 75082*


Treat Your Apprentices Like VIPs!

AFSA’s Virtual Instruction Program (VIP) for Apprentices is training that comes straight from our expert instructors. They lead the way to ensure your men and women are trained, letting you focus on OJT. Click here <https://www.firesprinkler.org/sprinkler-apprentice-training/>to learn more and enroll..



On Tue, Jan 31, 2023 at 9:16 AM Chris Dorn <[email protected]> wrote:

    The commodity that I am dealing with is solid piled group A
    plastics. Exposed, Expanded, Unstable, storage height  >5 ft to
    <12 ft with max ceiling height of 20’.

    The particular section of code which I am questioning is below.
    15.2.2.7(2) states that where table 15.2.2.5(a) allows densities
    and areas to be selected in accordance with Curve EH1 there are
    allowances for reduction of the hydraulic area to be reduced to
    2000 square feet if 8.0 high temperature heads are used by
    applying 15.2.2.7(2)(a). When I look at the section of table
    15.2.2.5 the density called out is .3gpm. This is the density for
    EH1 but is not called out as EH1 on table 15.2.2.5(a).  My feeling
    is that while the density called out is .3gpm it is not
    specifically called EH1 like some of the other densities in the
    same table. Therefore I should calculate 2500 square feet per
    15.2.2.7(a) and I cannot apply 15.2.2.7(2)(a). Agree or disagree
    and why?

    *15.2.2.7* *For Table 15.2.2.5(a) and Table 15.2.2.5(b), the design

    areas shall be as follows:

    (1) The area shall be a minimum of 2500 ft2 (232 m2).

    (2) Where Table 15.2.2.5(a) and Table 15.2.2.5(b) allow densities

    and areas to be selected in accordance with Curve

    EH1 and Curve EH2 of Figure 13.2.1, any density/area

    from the curves in Figure 13.2.1 shall be permitted. When

    selecting a point from the EH1 or EH2 density/area

    curves of Figure 13.2.1, the following area reductions

    shall be permitted:

    (a) For K-8.0 (115) sprinklers used with Curve EH1, the

    design area shall be permitted to be reduced by

    25 percent, but not below 2000 ft2 (186 m2), where

    high temperature sprinklers are used.


    _________________________________________________________
    SprinklerForum mailing list:
    https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
    To unsubscribe send an email to
    [email protected]


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to