The EC sprinklers are listed at a specific density, so you can't change that. You can calculate 2000 sq ft, but it will still be the minimum flow / pressure at a given spacing per the data sheet. Also, they are not listed for storage. So, they can not be used for storage applications.
Travis Mack, SET M.E.P.CAD | 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074 www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348 AutoSPRINK | AutoSPRINK FAB | AutoSPRINK RVT | AlarmCAD Book appointment time in my calendar https://calendly.com/t_mack_mepcad From: Dewayne Martinez <[email protected]> Sent: Wednesday, February 15, 2023 2:46 PM To: [email protected] Cc: Dewayne Martinez <[email protected]> Subject: [Sprinklerforum] Can OH II listed EC sprinklers be used for storage application? I have a customer that wants to store non-encapsulated ,Class II on single/double row racks with 8ft aisles. to 15ft high. When I work out the numbers and apply Fig 16.2.1.3.4.1 (NFPA 13, 2013ed) I get a density of 0.189/2000 for high temperature sprinklers. The original system was designed using extended coverage K14 sprinklers, 18x18 at OH 2 density. If I go up the OH2 curve to 2000 sq ft I get a 0.19/2000 density. Can I pick up the additional EC sprinklers for the 2000 sq ft at the required EHP for the OH 2 spacing and call it good if the calcs work? Thank you, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee, WI 53072 [email protected]<mailto:[email protected]> Ph: 262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com/ [cid:[email protected]]
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]