Thanks Travis,
I was just trying to convince myself that if it was still at or under the OH2 
curve and I am allowed to design anywhere along that curve it could still be 
called OH2.

Thank you,

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/

[cid:[email protected]]

From: Travis Mack <[email protected]>
Sent: Wednesday, February 15, 2023 3:49 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Cc: Dewayne Martinez <[email protected]>
Subject: [External]RE: Can OH II listed EC sprinklers be used for storage 
application?

The EC sprinklers are listed at a specific density, so you can't change that.  
You can calculate 2000 sq ft, but it will still be the minimum flow / pressure 
at a given spacing per the data sheet.  Also, they are not listed for storage.  
So, they can not be used for storage applications.


Travis Mack, SET
M.E.P.CAD |
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<https://link.edgepilot.com/s/82879486/cWBkTDBhYECX8h7rQfqBSg?u=http://www.mepcad.com/>
 | m: 480.547.9348

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

Book appointment time in my calendar
https://calendly.com/t_mack_mepcad<https://link.edgepilot.com/s/c6c1baa9/-yDGAv1XmECNIm1IGeQsnQ?u=https://calendly.com/t_mack_mepcad>

From: Dewayne Martinez 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, February 15, 2023 2:46 PM
To: 
[email protected]<mailto:[email protected]>
Cc: Dewayne Martinez 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Can OH II listed EC sprinklers be used for storage 
application?

I have a customer that wants to store non-encapsulated ,Class II on 
single/double row racks with 8ft aisles. to 15ft high.  When I work out the 
numbers and apply Fig  16.2.1.3.4.1 (NFPA 13, 2013ed)  I get a density of 
0.189/2000 for high temperature sprinklers. The original system was designed 
using extended coverage K14 sprinklers, 18x18 at  OH 2 density.  If I go up the 
OH2 curve to 2000 sq ft I get a 0.19/2000 density.  Can I pick up the 
additional EC sprinklers for the 2000 sq ft at the required EHP for the OH 2 
spacing and call it good if the calcs work?

Thank you,

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/<https://link.edgepilot.com/s/199820fc/wuTebtA6o0GSgxVwMTxYxw?u=http://www.total-mechanical.com/>

[cid:[email protected]]

CAUTION: This email originated from outside of the organization. Do not click 
links or open attachments unless you recognize the sender and know the content 
is safe.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to