Brian,

I would lean towards Repair Garage. The IBC specifically calls out storage of 
commercial motor vehicles as an S-1 occupancy with a reduced fire area 
requiring protection. The IBC assigns the same S-1 classification and fire area 
for repair garages so that gives a pretty good indication that they are a 
similar hazard and gives you a solid reasoning if you need to "show your work" 
since apparatus bays are specifically designated in NFPA 13.

Hope this helps!

Eric Rieve
Rieve Fire Protection

From: Brian Harris <bhar...@bvssystemsinc.com>
Sent: Thursday, February 16, 2023 2:54 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: Fire Station Apparatus Bay

Travis-
Would an Apparatus Bay be considered a Automobile Parking Showroom (OH1) or a 
Repair Garage (OH2)? We're still in 2013 edition.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Travis Mack <t.m...@mepcad.com<mailto:t.m...@mepcad.com>>
Sent: Thursday, February 16, 2023 2:48 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Fire Station Apparatus Bay

If you look at the 2022 edition of NFPA 13, you will see that automobile 
parking garages are OH2.


Travis Mack, SET
M.E.P.CAD |
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.mepcad.com%2f&c=E,1,1UOy-PAR_dU9fIRhYqdL4TwlqzmFeYVMlH0iBokhasf7UdVqUqxLSaIv6dphNaFylyGDN4u7eYsxZ2OcQfk8Xrwb6ElA9660vSLjzwIWqUqjXg,,&typo=1>
 | m: 480.547.9348

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

Book appointment time in my calendar
https://calendly.com/t_mack_mepcad

From: Brian Harris <bhar...@bvssystemsinc.com<mailto:bhar...@bvssystemsinc.com>>
Sent: Thursday, February 16, 2023 12:42 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Fire Station Apparatus Bay

I've seen Apparatus Bays in fire stations protected both as OH1 & OH2. Seems 
per code OH1 (car parking) would be appropriate?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,mfxWdUshm9BD7obLcPfGh2VqX7R-vIlir7EjI0gm8A3_x8dAfUyE9fFD4H0XZTfdGEK4DPn5okUl_avA34UysvJT7f-N6UOCfAzbSlQOB7-6UtQm&typo=1>
Phone: 704.896.9989
Fax: 704.896.1935


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to