The other responses line up quite well with what I understand of FM
Global guidelines.
I also point out to you that if you're going to follow FM Global Data
Sheet 8-9 for protection of storage you must - effectively - throw NFPA
13 in the trash and design and install the entire system in accordance
with FM Global guidance, which includes 2-0.
*Ken Wagoner, SET*
*Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235*
*Phone: (760) 745-6181 *
*Visit the website
<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>*
On 4/18/2023 2:12 AM, Phong - Indochine Engineering wrote:
Dear All,
I am having a problem when choosing in-rack sprinkler head with FM
approved, and having the right temperature.
As per FM Global Property Loss Prevention Data Sheets 8-9, March 2010
Interim Revision July 2021,
2.3.4.3 K-Factors, Nominal Temperature Rating, and RTI Rating of
In-Rack Storage Sprinklers
2.3.4.3.1 Use nominally rated 160°F (70°C) FM Approved in-rack
sprinklers for all in-rack sprinkler
installations.
I cannot find actual sprinkler head approved by FM and having this
rated 160°F (70°C), for example, this model of Viking (bulb type)
https://www.approvalguide.com/productDetail?productid=118279
Should I follow NFPA13,
Chapter 23 - ESFR Requirements for Storage Applications
23.4.4 Sprinklers shall be intermediate temperature–rated ESFR pendent
sprinklers with a nominal K-factor of K-25.2 (360).
Checking the Viking ESFR sprinkler head, it seems only the fusible
type is ranked as ESFR:
Early Suppression Fast Response (ESFR) | Viking Group Inc.
<https://www.vikinggroupinc.com/products/viking-fire-sprinklers/storage/esfr-early-suppression-fast-response-sprinklers>
But the temperature of Viking ESFR sprinkler head having FM approved
is also not rated 160°F (70°C), but 74°C and 96°C
FM3007275.PDF (vikinggroupinc.com)
<https://www.vikinggroupinc.com/sites/default/files/databook/sprinklers/storage/121aefm.pdf>
Please can you advise.
Regards,
Le Vu Phong
Indochine Engineering Vietnam JSC
Unit 12-01
Pearl Plaza
561A Dien Bien Phu Street
Binh Thanh District, HCMC, VN
Mobile: +84 (0) 902 363 525
Tel: +84 (8) 3512 4100
Fax: +84 (8) 3512 4108
Web: www.indoeng.com <http://www.indoeng.com/>
<http://www.linkedin.com/company/2077231>
<http://www.twitter.com/indoeng_>
<http://www.youtube.com/user/indochineengineering>
phong_indochineengineering
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email tosprinklerforum-le...@lists.firesprinkler.org
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org