The other responses line up quite well with what I understand of FM Global guidelines.

I also point out to you that if you're going to follow FM Global Data Sheet 8-9 for protection of storage you must - effectively - throw NFPA 13 in the trash and design and install the entire system in accordance with FM Global guidance, which includes 2-0.


*Ken Wagoner, SET*
*Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235*
*Phone: (760) 745-6181 *
*Visit the website <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>*
On 4/18/2023 2:12 AM, Phong - Indochine Engineering wrote:

Dear All,

I am having a problem when choosing in-rack sprinkler head with FM approved, and having the right temperature.

As per FM Global Property Loss Prevention Data Sheets 8-9, March 2010

Interim Revision July 2021,

2.3.4.3 K-Factors, Nominal Temperature Rating, and RTI Rating of In-Rack Storage Sprinklers

2.3.4.3.1 Use nominally rated 160°F (70°C) FM Approved in-rack sprinklers for all in-rack sprinkler

installations.

I cannot find actual sprinkler head approved by FM and having this rated 160°F (70°C), for example, this model of Viking (bulb type)

https://www.approvalguide.com/productDetail?productid=118279

Should I follow NFPA13,

Chapter 23 - ESFR Requirements for Storage Applications

23.4.4 Sprinklers shall be intermediate temperature–rated ESFR pendent sprinklers with a nominal K-factor of K-25.2 (360).

Checking the Viking ESFR sprinkler head, it seems only the fusible type is ranked as ESFR:

Early Suppression Fast Response (ESFR) | Viking Group Inc. <https://www.vikinggroupinc.com/products/viking-fire-sprinklers/storage/esfr-early-suppression-fast-response-sprinklers>

But the temperature of Viking ESFR sprinkler head having FM approved is also not rated 160°F (70°C), but 74°C and 96°C

FM3007275.PDF (vikinggroupinc.com) <https://www.vikinggroupinc.com/sites/default/files/databook/sprinklers/storage/121aefm.pdf>

Please can you advise.

Regards,

Le Vu Phong

Indochine Engineering Vietnam JSC

Unit 12-01

Pearl Plaza

561A Dien Bien Phu Street

Binh Thanh District, HCMC, VN

Mobile: +84 (0) 902 363 525

Tel: +84 (8) 3512 4100

Fax: +84 (8) 3512 4108

Web: www.indoeng.com <http://www.indoeng.com/>

<http://www.linkedin.com/company/2077231>

        

<http://www.twitter.com/indoeng_>

        

<http://www.youtube.com/user/indochineengineering>

        

        

phong_indochineengineering


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email tosprinklerforum-le...@lists.firesprinkler.org
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to